1)What will you do if main incomer VCB fail in your site ?
Answers were Sorted based on User's Feedback
Answer / vijay chander
first we informed to respective electricity office and then
find the fault inside the VCB or E.B side. if inside the
VCB means call the person from VCB manufetures.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / sskumar
Hai everybody,
Good and thanks to all of you for giving a ideas.But here
we should discuss only Technical matters not for
management.
So coming to the point, first we should cut off the
incoming supply to the VCB, how? first we should open the
AB switch, then automatically the supply wont come to VCB.
Then remove the VCB and rectify it.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / gunasekaran
if we have double bus system we can close the B/C unit and
get the supply from another bus
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / kanand078
if DG is there run the pland at dg load..after i will check
the fault and rectify
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / y.hari kishore babu
first we should cut off the incoming supply to the VCB, how?
first we should open the AB switch, then automatically the
supply wont come to VCB.
Then remove the VCB and rectify the problem by vendor or
myself with help of our tecnicians
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / g.kumaresan.
If Main incomer fail in our site Immediatly to Isolate the
incomming supply and VCB. Bec's to protect the inside Heavy
Equipment insite in our site, then to inform the situation
in our Authoriy officer, at the same time to ensure the
back feeding arrangement, Bec's can not maintain the supply
intruption in long time.
So, doing back feeding arrangement immediatly with our
higher authrity knowledge and also other officer sugection.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / anish salvi
If the incomer is further joint to transmission line Than no worry!! just Bypass the CB beacuse there are always CTs & pTS for the measurement purpose & in case if any fault occurs than even in absense of the Vaccum circuit breaker (used for 110KV and above)
Where as if it is the Distribution than use DO fuse for protection
| Is This Answer Correct ? | 0 Yes | 0 No |
In India why is the supply frequency 50hz? I need a particular answer for it..
why the electrical insulators suspention breakdowen
The iron loss in a 100kva transformer is 1 kw and full load copper losses are 2 kw, then what is maximum efficiency occure at a load?
why transformer is rated in kva?
what is the earthing condition between earth & neutral.
are you hear the meaning of burden , excat meaning of burden in only one word
Why do we need a separate control desk & PLC control panel in Boiler plant or coal handling plant? Can we provide cost effective Control desk cum PLC panel. Is there is an specific need for control desk.. kindly advice.
why transformer rated in KVA not in KW ? we know that W= v*i
what work will do diffrential realay DG set
0 Answers IG Petrochemicals Ltd,
What is the formula to calculate a three phase alternator
What is polarisation index value?.(pi value) Simple & brief definition of polarisation index?..
What is the lifetime of a Thyristor? Is there a recommended lifetime for thyristors after which they should be replaced?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)