1)What will you do if main incomer VCB fail in your site ?
Answers were Sorted based on User's Feedback
Answer / vijay chander
first we informed to respective electricity office and then
find the fault inside the VCB or E.B side. if inside the
VCB means call the person from VCB manufetures.
Is This Answer Correct ? | 10 Yes | 0 No |
Answer / sskumar
Hai everybody,
Good and thanks to all of you for giving a ideas.But here
we should discuss only Technical matters not for
management.
So coming to the point, first we should cut off the
incoming supply to the VCB, how? first we should open the
AB switch, then automatically the supply wont come to VCB.
Then remove the VCB and rectify it.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / gunasekaran
if we have double bus system we can close the B/C unit and
get the supply from another bus
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / kanand078
if DG is there run the pland at dg load..after i will check
the fault and rectify
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / y.hari kishore babu
first we should cut off the incoming supply to the VCB, how?
first we should open the AB switch, then automatically the
supply wont come to VCB.
Then remove the VCB and rectify the problem by vendor or
myself with help of our tecnicians
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / g.kumaresan.
If Main incomer fail in our site Immediatly to Isolate the
incomming supply and VCB. Bec's to protect the inside Heavy
Equipment insite in our site, then to inform the situation
in our Authoriy officer, at the same time to ensure the
back feeding arrangement, Bec's can not maintain the supply
intruption in long time.
So, doing back feeding arrangement immediatly with our
higher authrity knowledge and also other officer sugection.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / anish salvi
If the incomer is further joint to transmission line Than no worry!! just Bypass the CB beacuse there are always CTs & pTS for the measurement purpose & in case if any fault occurs than even in absense of the Vaccum circuit breaker (used for 110KV and above)
Where as if it is the Distribution than use DO fuse for protection
Is This Answer Correct ? | 0 Yes | 0 No |
what r the types of detectors? state the location these detectors?
Why Auto Transformer is called "Auto"? What is the logic?
what is the difference between earth and neutral?
56 Answers Bhel, Emerson, HCL, JLL, L&T, Siemens, TVS,
why do we provide metallic enclosure to bus duct and then ground it?
what is difference between electrical and electronics
Send me Model Question paper for the post Scientific Assistant in NPCIL
For a Potential Transformer(PT), the primary neutral terminal must be grounded before energization. Why....? What will be heppend if we energize the PT without grounded the primary neutral point? Why..........?
Differentiate between ideal and non ideal current sources?
How to select the Cable size for 550 Amps Load without seeing the cable Catalogue?
i am having a 3 phase 12.5HP motor,that is connected in Star/delta.Without any Trip that motor stopped suddenly why?
800A 22KV TP OCB. explain
What is purpose of reactor?.What is different between line and bus reactor?