1)What will you do if main incomer VCB fail in your site ?
Answers were Sorted based on User's Feedback
Answer / vijay chander
first we informed to respective electricity office and then
find the fault inside the VCB or E.B side. if inside the
VCB means call the person from VCB manufetures.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / sskumar
Hai everybody,
Good and thanks to all of you for giving a ideas.But here
we should discuss only Technical matters not for
management.
So coming to the point, first we should cut off the
incoming supply to the VCB, how? first we should open the
AB switch, then automatically the supply wont come to VCB.
Then remove the VCB and rectify it.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / gunasekaran
if we have double bus system we can close the B/C unit and
get the supply from another bus
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / kanand078
if DG is there run the pland at dg load..after i will check
the fault and rectify
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / y.hari kishore babu
first we should cut off the incoming supply to the VCB, how?
first we should open the AB switch, then automatically the
supply wont come to VCB.
Then remove the VCB and rectify the problem by vendor or
myself with help of our tecnicians
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / g.kumaresan.
If Main incomer fail in our site Immediatly to Isolate the
incomming supply and VCB. Bec's to protect the inside Heavy
Equipment insite in our site, then to inform the situation
in our Authoriy officer, at the same time to ensure the
back feeding arrangement, Bec's can not maintain the supply
intruption in long time.
So, doing back feeding arrangement immediatly with our
higher authrity knowledge and also other officer sugection.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / anish salvi
If the incomer is further joint to transmission line Than no worry!! just Bypass the CB beacuse there are always CTs & pTS for the measurement purpose & in case if any fault occurs than even in absense of the Vaccum circuit breaker (used for 110KV and above)
Where as if it is the Distribution than use DO fuse for protection
| Is This Answer Correct ? | 0 Yes | 0 No |
CT Ratio of a energy meter connection is Red Phase : 100/5A, yello Phase : 50/5A & Blue phase : 100/5 A what is the overall Multiplication factor
what is MULTIPLYING FACTOR in substations??
what is the pre commissioning test to be carried out on LT power panel at site?
Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups ac supply only.
12 Answers ACC, JLL, ZETDC,
State kirchoff current law?
what is meant by reactive power ,active power & real power ? thank you
Why silica gel use?
What is the safety factor is to be consider while selecting the switchgear and protection for electrical system
What is maximum rating of transformer ?
why semicondoctor use in HT cable?
What are the main Electrical IS rules?
X/R ratio in 11kv transmission line is?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)