Could anyone clarify my wondering.
What is the difference between knee point voltage and
saturation voltage of the CT.
Is their any formula to calculate these values?
Answers were Sorted based on User's Feedback
Answer / john bosco
knee point voltage definition
when applying voltage in secondary gradually from zero
and measuring current for step voltages, the current raise maintains constant slope up to some level of voltage.
for further raise in voltage secondary current raise do not follow the slope.
the voltage from which 10 % raise gives 50% raise in secondary current called as knee point voltage of current transformer(IEC standard)
saturation voltage is maximum secondary voltage developed across ct for any primary current
protection class CT
formula for VK= Is.ALF.(Rct+Rb)
Is- rated secondary current
ALF- accuracy limit factor
Rct- measured secondary resistance
Rb - rated burden of CT
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / thowsif_emerson_csm team
The knee point
is a ten percent ratio error between the
primary input current and the corresponding secondary
output current.
The saturation point involves determining the secondary
voltage necessary to drive the measured current through the
impedance of the secondary circuit.
For More Details,Pls visit
http://www.control.com/thread/1026243854
| Is This Answer Correct ? | 1 Yes | 1 No |
How to calculate current carrying capacity of copper conductor _ such as cable size 25sq mm,50 sq mm, 75 sq mm, 100 sq mm
Explain what is Zener diode?
How to Convert horsepower to kva? what is the three phase formula? email me if u know thanks Rehan smileavail@msn.com
WHAT IS VFD,FUNCTION, PURPOSE,
My meter CT is 200/5amps Then my electrical meter MF=???please suggest
Is there any guideline say about display of earthing value near to earth pit
If the kvar rating of capacitor bank is 600 kvar at 525V then what it's rating at 415v.
Why used IGBT IN AC Drives
Differnce between Analog & Digital
why colour of electrical equipment( like transformer) is grey
The power factor of the fixed load is 0.8, now the p.f is varying from 0.8 to 0.5.
A rotor of an induction machine is delta connected. Now is there any necessacity to short the slip rings?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)