I've heard that most of the substations are rated in
multiples of 1.11 because of form factor.What is form factor?
Answers were Sorted based on User's Feedback
Answer / vikash
Form Factor= R.M.S value / Average value of current
= 1.11
R.M.S value stands for root mean square. It is defined as DC component of ac current which produces heating effect.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / prakash
why it is multiple of 11 means 10% considered as line loss
that why all voltage are in multiple of 11 11kv/33kv/66kv
Is This Answer Correct ? | 2 Yes | 1 No |
why reactive power control is required
to operate air conditioner of 1.5ton what power of generator is required
sail kaott diploma ece ke interviw me qus.kis parkar ke aate hai aur G.S me kya puchate hai kya sameedyaan me kis parkar ke qu.puchate hai
At what voltage domestic tubelight works?
explain single phase series motor
what is the difference between metalhalide and mercury vapour lamp
Why battery is always operate on dc supply?
1 Answers Vikram Ispat Industries,
WHAT SHOULD BE THE BEST CURRENT RATINGS (PRIMARY / SECONDARY)FOR A CT INSTALLED AT THE INCOMING 11KV PANE? WILL IT BE CALCULATED ON THE BASES OF MAXIMUM DEMANT VALUE OR ON SUM OF ALL TRANSFORMER'S KVA? NOMALLY MAX DEMAND REPRESENT THE MAXIMUM OPERATING LOAD OF THE PLANT AND TOTAL KVA OF (SAY 5 NUMBERS TRANSFORMERS) REPRESENT THE CONNECTED LOAD. WHICH i.e. MAX DEMAND KVA OR CONNECTED KVA ARE BETTER TO USE FOR CT CURRENT CALCULATION? PLEASE ANSWER.
where is used dc volage transformer,and what is highest capacity of transformer
whydoes the p.f of diesel generator always be 0.8 explain how will you determine the shortcircuit capacity of network
why 15 kw motor winding resistance is low then 5 kw motor winding resistance?
1.what is meaing of ups,and used in softwares and sud stations,and main partes in ups. 2.main partes of the Disel Genarator. 3.main partes of the chiller and safty equipments.