how we can improove power factor?????????
Answers were Sorted based on User's Feedback
Answer / sujay aich
Power factor can be improved by using static capacitors or
synchronous motors.
| Is This Answer Correct ? | 34 Yes | 1 No |
Answer / raju_
WECAN IMPROVE POWER FACTOR BY USING CAPACITER BANK AT
RECIEVING STATION IN POWER STATION & ALSO WE USE THE
SYNCRONOUS MOTER AS SYNCRONOUS CANDENSER IN POWER STATIONS.
| Is This Answer Correct ? | 24 Yes | 2 No |
Answer / thowsif_emerson_csm team
APFC Panels:-
An automatic power factor correction unit is
used to improve power factor. A power factor correction
unit usually consists of a number of capacitors that are
switched by means of contactors. These contactors are
controlled by a regulator that measures power factor in an
electrical network. To be able to measure power factor, the
regulator uses a current transformer to measure the current
in one phase.
Depending on the load and power factor of the network, the
power factor controller will switch the necessary blocks of
capacitors in steps to make sure the power factor stays
above a selected value (usually demanded by the energy
supplier), say 0.9.
Syncronous Condenser:-
Instead of using a set of switched
capacitors, an unloaded synchronous motor can supply
reactive power. The reactive power drawn by the synchronous
motor is a function of its field excitation. This is
referred to as a synchronous condenser. It is started and
connected to the electrical network. It operates at full
leading power factor and puts vars onto the network as
required to support a system’s voltage or to maintain the
system power factor at a specified level.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / gaurang bhavsar
Power factor can be improve by Automatic power factor
correction panel(APFC panel)in which power capacitors are
there depend on load power capacitors can be run with the
help of Contactors,From Synchronous condensor and Static
capacitor we can improve power factor upto 0.99 to 1.00
| Is This Answer Correct ? | 6 Yes | 0 No |
A Thyristor based unit called SVS Schemes,that is Static
VAR System is also use to inprove the POWER factor.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / animesh das
POWER FACTOR CAN IMPROOVE BY STATIC CAPACITOR & SYNCHRONOUS
MOTOR AS WELL AS INDUCTION MOTOR AT INSTANT.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / abhijeet..
we can improv pf by using synchronus motor or condeser bank
at reciving end
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / azhar
power factor can be improved by using phase advancer in
induction motor.
| Is This Answer Correct ? | 3 Yes | 10 No |
Why capacitor is blow when I am starting motor ?
why are we adopting 132kv,220kv for transmission rather than using 440kv at all transmission lines as it gives lower losses?
Hello, I am just preparing my self for a university interview and struck on the 11kv ring main unit system network. I just know that ring main unit has total three breakers, fuses and use to supply a power to any load/ building without any interrupt. But i am not be able to visualize the connections, either Ring main unit getting power from two different power sources? or there is always one feeder in complete ring circuit??? I would be highly thanks full of you help me.
i have 2 motor of same rating. on no load condition one motor take 1.6A but other motor is taking 4.8A. what is the reason of this. please explain with proof.
what is difference between KW,KVA,KVAR? also give me the formula for all the three...
In neutral the current will flow or not?
what is pf. how to calculate capacitor bank value to maintain unity pf.
18 Answers JH, Saint Gobain, Supreme Treves,
draw the full wave and half wave circuit of 3 phase system and inverter circuit used in ups
Please clarify, 1. Is it required to lay two runs of GI wire along with Armoured LT cable if it is laid between one big mains (63Amps TPN SDF) to small main (32A TPN SDF) with proper glanding termination? 2. If the armoured cable with proper glanding is laid from DB to CNC machine, is it required to run two runs of body earthing to the Machine from DB? 3.If the armoured cable with proper glanding is laid from Substation to Hangar, distance is approx. 100 mtrs, is it required to do earthing at shop area though the primary termination at substation is earthed through gland.
What is the working principle of VFD
what is the difference b/w ground & virtual ground?
Which of the following connection is best suited for 3-ph, 4 wire system A delta-delta B star-star C delta-star D star-delta
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)