Why we are putting off the APFC(automatic power factor
control) panel while the generator is running?
Answers were Sorted based on User's Feedback
Answer / ns
we are putting in APFC off condition in Generator running
because capacitor bank added in dg running condition power
factor increase and kva is more then its rated DG kva bcz
all generators desigen in 0.8 pf with rated Kva.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
APFC is for use while gen is running only.It is not
preferred as it may lead to voltage rise whenever there is
sudden network failure.
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / k.prakashchandra
Add that APFC is to be used only when gen is connected to
grid or network.
Is This Answer Correct ? | 0 Yes | 3 No |
what is droop?
what should be 3phase motor capacity or rating to connect in star connection. what should be 3phase motor capacity or rating to connect in delta connection. what should be 3phase motor capacity or rating to connect in star delta connection
why capacitor is placed in fan
The initial current is very large at the time of starting for almost all DC motors. SO WE USE STARTER FOR A SAFE STARTING but at our homes we don’t see any starters in our coolers, motors.WHY DON’T WE NEED STARTERS FOR THESE APPLIANCES?
why fan consume constant power even when we increase or decrease its circuit resistance through speed regulator???
If two transformers same rating(11KV / 440V)connected in the same primary line(11KV), can we connect(bus coupler) secondary side directly or need a synchronization????
why CRGO material used in transformer?
what is meant by poly phase induction motor ? how its operating by single phase or three phase?
How much current can a 3-1/2 core 100 mm wire carry?
3 Answers Epitome, Focus, Focus Energy,
what is advantage of providing taping on HT side?
What are protection of transformer on HT side & on LT side?
Can HT cable(11kv cable) be used for 415V, 700A requirement.