how to calculate the powerfactor in induction motor having
name plate details? for example 1 h.p motor 1.86 A 415 V
Answers were Sorted based on User's Feedback
We know P=VICOSф.
Here, P=1H.P=746W,V=415v,I=1.85amp
Now putting this value on the equation simply we get the PF.
746=415*1.85*COSф
746
=>COSф=----------=0.9716 and it must be lagging.
415*1.85
More info: Earn and Learn pls visit
http://a2zengineering.blogspot.com/
Is This Answer Correct ? | 18 Yes | 2 No |
Dear Zakir husan
What is 1092 in your equation .
That we know that
p=root3 v*i*cos phi
1 h.p =746 watts = 1.732*415*1.86*cos phi
cos phi= 746/1.732*415*1.86
= 0.55 and pf leging.
Is This Answer Correct ? | 12 Yes | 3 No |
Answer / aaaa
its depend on phase no of the motor.(3-phase , single phase)
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / vishnu
here P=1H.P=746w,
I=1.86,
V=415V
FORMULA P=1.732*V*I*COS phi
cos phi=746/1.732*415*1.86
cos phi=0.55
Is This Answer Correct ? | 9 Yes | 5 No |
Answer / jagjeet
Dear Satish
The power factor dependent on the loading factor of the
induction motor , You can measure the Line current and apply
the formula suggested by Zakir or you can refer the
characteristics charts of Motor to find out the Power Factor.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / shakus
@Sakthish_kumaar
Please mention whether the motor is single phase or three
phase?
apply for single phase>>
P=VIcosØ
and Apply for three phase>>
P=√3VIcosØ
Is This Answer Correct ? | 2 Yes | 0 No |
what is relation between vector group of transformer and its load hormonics?
What is meant by stator?
How to calculate the input cable rating for 10kva ups (3phase input and single phase output and also 3phase output, battery rating 65Ah)provide the formula also.thnx
what is the formula for calculation of sac?
WHY AREWE USING THE 3 1/2 CORE CABLES IN POWER TRANSMISSION
1 Answers Phoenix Technologies,
How is the gain affected by the introduction of feedback in a control system.
why we use salt for earthing?
in thermal power plants by opening the turbine governor valve increase the generator load. how
what is the relation between the leading pf and supply voltage?
There is 15 KVA UPS using for single phase load.And 30 batteries of 12 V, 100 Ah are connected in series. Load is taking 15 A current.What will be the back up power for this UPS on same load?
1 Answers BS, Dynamic Software,
what is ripple component in ac supply?
How much depth n width required for laying of 1X70 Sqmm Cable in Desert???
0 Answers Alka Electromech, Aramco,