how to calculate the powerfactor in induction motor having
name plate details? for example 1 h.p motor 1.86 A 415 V
Answers were Sorted based on User's Feedback
We know P=VICOSф.
Here, P=1H.P=746W,V=415v,I=1.85amp
Now putting this value on the equation simply we get the PF.
746=415*1.85*COSф
746
=>COSф=----------=0.9716 and it must be lagging.
415*1.85
More info: Earn and Learn pls visit
http://a2zengineering.blogspot.com/
| Is This Answer Correct ? | 18 Yes | 2 No |
Dear Zakir husan
What is 1092 in your equation .
That we know that
p=root3 v*i*cos phi
1 h.p =746 watts = 1.732*415*1.86*cos phi
cos phi= 746/1.732*415*1.86
= 0.55 and pf leging.
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / aaaa
its depend on phase no of the motor.(3-phase , single phase)
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / vishnu
here P=1H.P=746w,
I=1.86,
V=415V
FORMULA P=1.732*V*I*COS phi
cos phi=746/1.732*415*1.86
cos phi=0.55
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / jagjeet
Dear Satish
The power factor dependent on the loading factor of the
induction motor , You can measure the Line current and apply
the formula suggested by Zakir or you can refer the
characteristics charts of Motor to find out the Power Factor.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / shakus
@Sakthish_kumaar
Please mention whether the motor is single phase or three
phase?
apply for single phase>>
P=VIcosØ
and Apply for three phase>>
P=√3VIcosØ
| Is This Answer Correct ? | 2 Yes | 0 No |
Why most of analog o/p devices having o/p range 4 to 20 mA and not 0 to 20 mA ?
what is meant by negative sequencing in power system.explain in detail
why fan consume constant power even when we increase or decrease its circuit resistance through speed regulator???
I Have 3 Phase 10 KW AC Alternator i found one phase weak, so what will be the reason & what action shouls i take to rectify the same.
how is reactive power controlled on the transmission system
What is the function of the circuit breaker failure relay?
15 kva dg set single phase takes 63amp( approximate) while same rating 15kva three phase takes 35amp approximate. why ? and what will be per phase current for 15 kva
which electrical supply used for long distance traction 1.1-ph 22kv a.c 50hz 2.2-ph 22kv a.c 50 hz 3.dc vtg 4.1-ph 22kv 150 jhz
What is the function of PMG in DG sets & how it works??????????
Does the direction of rotation of d.c. Shunt motor would get reversed if the armature current and field current both are reversed?
I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.
when turbine trips generator will becomes induction motor or synchronous motor?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)