What is FM200 Fire Supresion System??
Answers were Sorted based on User's Feedback
Answer / ramendra shukla
FM 200 is fire supresion system which is used to neutralise
the fire in closed areas.Normaly it is used in Data Centre,
server room or very critical areas of facility due to its
cost.
FM200 is name of Gas.When it is mechnically dressed
with ,Cyilender, nozzel,connecting pipes,support &pressure
switch called FM200 system.and mainly used in very critical
area of facility like-Servsr room,data Center ,and for very
imporant set up due to gas cost.
Funtion: when ther will be fire the gas releases on closed
area FM200 gas is having capability to minimize the absence
of Oxygen &as we know absence of oxygen fire can not take
place.
| Is This Answer Correct ? | 28 Yes | 2 No |
Answer / suhana_t
The FM-200 Fire Suppression System is an engineered system
utilizing
a fixed nozzle agent distribution network. The system is
designed
and installed in accordance with the National Fire
Protection
Association (NFPA) Standard 2001, “Clean Agent Fire
Extinguishing
Systems.” When properly designed, the FM-200 system will
suppress
surface burning fire in Class A, B, and C hazards.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / sandeep.sekharan@yahoo.com
Heat absorption is the main extinguishing property of FM 200 system and oxygen replacement is secondary.
| Is This Answer Correct ? | 1 Yes | 0 No |
Draw a SLD for main panel for school having connected load of 1200kw and emergency generator 200kw.also show the increase of additional load of chiller 225kw in the lv panel indicating meter postion size of transformer ,cables and capacitor bank.
How does flights get the neutral(grounding)
Define characteristics impedance?
what will happen if a cw rotating altenator being synchronized to ccw rotating altenator
Wat will happen if R-phase of an alternator is connected to B- Phase of AMF panel fed from alternator
We have a bank capacitor rating of 60 KVAR for a overall load of 160 KVA and we have connected three loads of 50KVA each. We would like to auto matically correct PF using APFC. How do we design it?
how do you choose the cable size as per amps rating & the voltage drop for the same.
Sir pl provide 5 year sample paper for post junior engineer(electrical).I have currently applied for junior engineer (electrical) on RRB Ajmer
how a generating station can monitor its multi users power factor. What type of incentive /penalty is associated with power factor management.
How many earthing pits required for diesel generator set ? Why ?
WILL SCHNEIDER MAKE ACB(MASTERPACT)TRIP ON REVERSE POWER?
How i can identify the 220V and 110V power supply equipment? No tag number.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)