what to do with nuetral when Generators are running in
parrellel
Answers were Sorted based on User's Feedback
Answer / guest
First generator need to connect ,while second generator
nuetral kept open
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / rajesh anne
any one of the generator neutral need to be grounded.if it
is multiple generators also one generator neutal must need
to be grounded because the unbalnce currents will pass
through the neutral while it was running in parallel.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / muninanjappa
First Generator must be grounded and next generator neutral
must be left open works as floating neutral.
Both Alternator neutrals should not be earthed while running
in parallel
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / b madhu sudhan reddy
when two genarators are conected in parllel then it must
satisfy the synchronisam i.e it must satisfys certain
conditions.suppose when it falls to out of synchronisam
then there is chance of occuring the fault i.e there is a
chance for circulating high currents,at that particular
situtation the nutral will help for flowing that currents
to ground&it also protect the system when the lightning is
occur
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sreeraj n
the generator ,which we first connect to bus ,that generator nuetral need to connect to load ,other generators nuetral kept open
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mallikarjuna reddy
I Hope we have to connect the both neutrals(individual
alternators)to the earth.if fault occurs when that
synchronism fails unbalance currents will flow through this
neutarl to ground.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / b.ramesh babu
when the generator satisfing the parallesm conditions then
the neutral is grounded because when when the parellelism
conds are not satisfied then the circulating currents are
generated which become one become motor and other become
generator..........so d circulatind currents are flow to
the grounded..
| Is This Answer Correct ? | 0 Yes | 2 No |
what is load shedding
why did youi choose this career?
can we use the same fuse for both ac and dc?
what is the earth resistance ?
2 Diesel Generators 900KVA connected to the bus bar for essential load as an alternative for power taken from 11/440V 3KVA Transformer supplying this bus bar. my question here is in the event of power failure on 11KV side can I feed the power to 11 KV bus by using the same transformer as reverse feed, what will be the inrush current???
How can calculate the daily electrical consumption of 7.5 HP motor, if the moter runs 24 hrs continiously. Also have to know about 3.5 hp chiller.
what is split phase ac system?
why names such like dog ,rabbit, osprey,ant are used for conductors.
anybody can give the voltage value for 1M ohm
i have a roll dia aprox.43 inches and gear box ratio is 14.3.so my question is how was decide the kw rating of motor.
what will happen if dc motor given ac supply
If 22 KV HT line, Current transformer is 25/5 then how to calculate multiplying factor.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)