We have 3 Gensets 1.500kva,2.380kva,3.250kva How can we
connect in common busbar&we have variable load.
Answers were Sorted based on User's Feedback
Answer / vishvesh
yes, we can connect this three generators in one busbar,
after fulflling following conditions.
1.voltage should be same.
2.frequency should be same.
3.phase sequence should be same.
after shynchronizing of all three outputs, we can
connect it to the common busbas.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / guest
we have to synchronise 3 dg for busbar connection.basic
conditions r
1.freq of all dg should be same.
2.phase seq shold be same.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / milinda4p
to connect 2 or more generators to a common bus those
generators should be synchronised.it means
1. frequency should be same (every generator should operate
in same frequency)
2.voltage magnitudes should be same at each bus (i:e if the
generators have different rated voltage outputs correct
transformers should be used to get the same voltages at the bus)
but the POWER RATING is not going to cause any problem for
synchronizing
But in supplying a load after connecting it is important to
adjust the power supplied according to the load.( should
maintain the frequency of the system in constant value. if
not the rotor speeds of the generators should go up or down
causing and destruction or stopping of generators )
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / n rajesh
No,because the following points should be taken,
1.Phase sequence should be same.
2.voltages should be the same.
3.Frequency should be same.
4.Power rating should be same.
| Is This Answer Correct ? | 0 Yes | 3 No |
In India,we use 230V,50HZ,where as many other countries use 110V,60HZ what r d advantages and disadvantages of each of them?
how to calculate of which rating transformer should be selected? take any example
what is high voltage in india?
if two transformers are placed parallel & both have fault impedance of 50KA will it increase or decrease show example?
Safety of on line ups
0 Answers Bhushan Power Steel, GE,
HOW TO CALCULATE THE ILLUMINATION IN INDOOR LIGHTING?
What are the causes for the failures of sandwich type (Al) busducts?
What is Plank's Law?
What is the Frequency while we step up the voltage from 220V to 11KV? Is it possible? Explain it?
How to calculate the value of earth capacitance in a transmission line.
What is meant by Active and reactive power?
8 Answers Micron Electricals, SVIT,
if you asked to choose a ckt breaker from MCB & MCCB for 32A which one will be best and why??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)