Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


We have 3 Gensets 1.500kva,2.380kva,3.250kva How can we
connect in common busbar&we have variable load.

Answers were Sorted based on User's Feedback



We have 3 Gensets 1.500kva,2.380kva,3.250kva How can we connect in common busbar&we have varia..

Answer / vishvesh

yes, we can connect this three generators in one busbar,
after fulflling following conditions.
1.voltage should be same.
2.frequency should be same.
3.phase sequence should be same.

after shynchronizing of all three outputs, we can
connect it to the common busbas.

Is This Answer Correct ?    12 Yes 0 No

We have 3 Gensets 1.500kva,2.380kva,3.250kva How can we connect in common busbar&we have varia..

Answer / guest

we have to synchronise 3 dg for busbar connection.basic
conditions r
1.freq of all dg should be same.
2.phase seq shold be same.

Is This Answer Correct ?    9 Yes 0 No

We have 3 Gensets 1.500kva,2.380kva,3.250kva How can we connect in common busbar&we have varia..

Answer / milinda4p

to connect 2 or more generators to a common bus those
generators should be synchronised.it means
1. frequency should be same (every generator should operate
in same frequency)
2.voltage magnitudes should be same at each bus (i:e if the
generators have different rated voltage outputs correct
transformers should be used to get the same voltages at the bus)

but the POWER RATING is not going to cause any problem for
synchronizing

But in supplying a load after connecting it is important to
adjust the power supplied according to the load.( should
maintain the frequency of the system in constant value. if
not the rotor speeds of the generators should go up or down
causing and destruction or stopping of generators )

Is This Answer Correct ?    0 Yes 0 No

We have 3 Gensets 1.500kva,2.380kva,3.250kva How can we connect in common busbar&we have varia..

Answer / n rajesh

No,because the following points should be taken,
1.Phase sequence should be same.
2.voltages should be the same.
3.Frequency should be same.
4.Power rating should be same.

Is This Answer Correct ?    0 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

Shall I use 40A semiconductor Fuses in 32 A SFU ? Frame size is same. What Happen if Fuses burn on SFU?

0 Answers  


Explain the terms real power, apparent power and reactive power for ac circuits and also the units used.

0 Answers  


what is the HT motor current setting (Motor protection relay)aganist FLA If the capacitor is connected in parallal to the motor to increase the P.F from 0.89 to 0.99. the setting is to be reduced. what is the formula for to calculate the current.(FLA - CALCULATED CURRENT!= )

1 Answers  


how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on star-delta starter?

6 Answers   HCC, L&T,


For which purpose the temp. rise test of transformer is conducted?

2 Answers  


why does in transformer the v/f ratio constant?

2 Answers   TATA,


Define the term Capacitance and Inductance?

0 Answers  


Dear all,recently in our plant we installed a conveyor for this the motor ratings are 5 hp and Amps 7.39.Due to on urgent starting of conveyor we fix the DOL starter with range of 9-15 amps.give me suggestion regarding on this issue

1 Answers  


Why an ac systems are preferred over dc systems?

0 Answers  


what is motor capacity of 80TR chiller? and also say what is the formula related temperature, motor capacity, TR?

0 Answers   Apotex, Periyar Chemicals,


why double earthing is required for welding machine & electrical tools.

7 Answers  


Why are tertiary windings used in transformers?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)