how to find motor contactor rating and bimetalic relay
rating? of 30kw motor which will operate on star-delta
starter?
Answers were Sorted based on User's Feedback
Answer / elangovan t
You can use Type2 coordination table to find out the
contactor rating and OLR rating.
Normally the OLR should be set at the Full load current
rating of the motor. Hence the OLR may be selected such that
the motor flc lie in the mid range of the relay span
| Is This Answer Correct ? | 17 Yes | 2 No |
Answer / ashish
FOR 30 KW MOTOR CONTACTOR RATING IS AS PER KW MENS 1 KW FOR
1 AMP CONTACTOR FOR SD STARTER FOR 30 KW MOTOR 30 AMP
CONTACTOR AND RELAY SET ON MOTOR FULL LOAD AMP. MULTIPLY BY
(.64).
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / aksx
how to find relay range and relay setting of three phase induction motor of 30kw ratting.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thakur
Full Load Current of Motor-52Ampas per(415.1.732.0.8)
Usually we are using any protective divece/conducter 1.5
time of higher side.then Contactor Carrying Capacity Will
be-80amp and Over Load relay Capaciry wil be-80 Amp and its
over load setting will be-30 amp as per (LI/1.732)
| Is This Answer Correct ? | 10 Yes | 13 No |
Answer / abhijit
as 30kw is rating flc=52 bmr relay setting will be 50 as it
should be slightly less than flc,contactor should be more
than flc but it depends upon the application coupling
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / sanjay
40 hp motor full load current appx 52amps so we have use
2.5 times relay rating and power contactor rating.
| Is This Answer Correct ? | 9 Yes | 26 No |
How the earth fault relay works please explain?????????
what is use of governer in diesle engine
EHV current carrying parts need to have smooth finish,then how can a 245kv GIS with emery finish can run so long?
The reason why the sending end and receiving end voltage sare almost equal when capacitive load is added.
what is the distance b/w EHV lines? 1.8m 2.11m 3.4m 4.14m
What is diversity factor and how to calculate it
2 Answers Al Faraa, Amul, Pentagon, Sobha Developers,
for 500mw power production how many range of transformer set in unit please reply if three transformer use .
WHAT IS THE USE OF STARTER AND CHOKE IN TUBE LIGHT?
what is priming pump?why it is used ?
i have 400/230v transformer and didnt done the neutral eatrhing. i connected one lamp to one phase and neutral to the earth. but the lamp is not glowing. again i connected neutral to earth and repeated the same. then the lamp is glowing. in the first condition i tested with a line tester also, at that time the tesrer is glowing what is happening i dont know can any one help me?
plz explain TSM and PSM.with example suppose ct ratio is 4000/5 and tsm is .15 and plug is at 3.75 if fault current is 8000A.so how i find relay oprating time.
2 Answers College School Exams Tests, ME,
what are balanced and unbalanced loads
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)