how to find motor contactor rating and bimetalic relay
rating? of 30kw motor which will operate on star-delta
starter?

Answers were Sorted based on User's Feedback



how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / elangovan t

You can use Type2 coordination table to find out the
contactor rating and OLR rating.
Normally the OLR should be set at the Full load current
rating of the motor. Hence the OLR may be selected such that
the motor flc lie in the mid range of the relay span

Is This Answer Correct ?    17 Yes 2 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / ashish

FOR 30 KW MOTOR CONTACTOR RATING IS AS PER KW MENS 1 KW FOR
1 AMP CONTACTOR FOR SD STARTER FOR 30 KW MOTOR 30 AMP
CONTACTOR AND RELAY SET ON MOTOR FULL LOAD AMP. MULTIPLY BY
(.64).

Is This Answer Correct ?    4 Yes 4 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / aksx

how to find relay range and relay setting of three phase induction motor of 30kw ratting.

Is This Answer Correct ?    0 Yes 0 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / thakur

Full Load Current of Motor-52Ampas per(415.1.732.0.8)

Usually we are using any protective divece/conducter 1.5
time of higher side.then Contactor Carrying Capacity Will
be-80amp and Over Load relay Capaciry wil be-80 Amp and its
over load setting will be-30 amp as per (LI/1.732)

Is This Answer Correct ?    10 Yes 13 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / abhijit

as 30kw is rating flc=52 bmr relay setting will be 50 as it
should be slightly less than flc,contactor should be more
than flc but it depends upon the application coupling

Is This Answer Correct ?    1 Yes 4 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / sanjay

40 hp motor full load current appx 52amps so we have use
2.5 times relay rating and power contactor rating.

Is This Answer Correct ?    9 Yes 26 No

Post New Answer

More Electrical Engineering Interview Questions

How to covert the ac to dc and how to control the dc output?

3 Answers   ABB,


How to distinguish between the armature wires with the field wires of a Dc motor ?

5 Answers  


What is the function of Lightning Arrester & Wavetrap in Power system ??

18 Answers   ABB, Bhel, Energy Infratech, Infosys, NTPC,


i) in which cases should we go for neutral and where should we go for ground? ii) in domestic supply we are getting 230v a.c.and what is the amount of current?

2 Answers  


What is a parabolic signal?

0 Answers  






a solenoid of inductance 250mH and resistance 10ohm is connected to a battery. the time taken for the magnetic energy to reach 1/4th of its maximum value will be?

1 Answers   SSC,


How colour picturetube works & how many year it will works.

0 Answers  


what is soft starter?working principle?where it can use?

3 Answers  


how can calculate resistance box for 15 kw, 6 pole, RV-230, RA-42 motor

0 Answers  


draw the restricted earth fault protection circuit install on power transformer and identify its parameters and draw C/C curve of it

0 Answers  


How to Calculate KA Rating of Main LT Panel

0 Answers  


what is difference between c-power & u-power air circuit breaker?

2 Answers   Areva, IIT, Marine Electricals,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16631)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1094)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)