At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC
54A as per the nameplate. At the time of starting it draws
840A instead of 390A (7.2%). As per the data sheet also its
390A starting current. it thru a dol starter from the MCC.
can anyone tell what is the problem in the motor
Answers were Sorted based on User's Feedback
Answer / ranjan prasad
From the question motor terminal connection is not known.
However this problem may arise if you will connect the
motor in delta instead of star. First check the terminal
connection of motor, if it is in star, connect in the same
manner.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / kannapa
do not use dol starer above 2.2kw rated motors
use star to delta starter it can withstand.
check also connections.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / r.v.giribabu
First Check the healthyness of the motor.
1. Check the winding resistence
2. Check insulation resistance using megger.
3. Check the bearing and apply the lubricant as applicable.
4. Check the healthyness of connected load.
Follow above steps adn yoiu will identify the problem.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / wani y.s.
First Check the healthyness of the motor -
1. Check the winding resistence
2. Check insulation resistance using megger.
3. Check the bearing and apply the lubricant as applicable.
4. Check the healthyness of connected load.( It should not
locked etc.)
5. If all above is OK. Then remove the motor from load &
ensure it is starting in ideal condition.( Hope connections
you are following up as given on the nameplate)
If it is starting in no load that means load GD squre is
high. Motor is taking longer time to start.You have to
select proper heavy duty DOL starter to withstand the
longer starting time. But ensure that motor is having
thermal time capacity to withstand this time.
7. You can also go for VFD as a starter this will definetly
will solve your problem no need to take care of thermal
time of the motor. Only select proper VFD to suit starting
torque of your application.
Is This Answer Correct ? | 0 Yes | 1 No |
pl. check motors connection in terminal box if it is
connected in star then current may increased.
Is This Answer Correct ? | 5 Yes | 13 No |
how you connect the induction motor first in star and then delta in star-delta starter
The following equipment are installed ia a plant 1. 110KW Induction motor 4 Nos 2. 30 HP motor 3 Nos 3 15 HP Motor 3 Nos 4 7.5 HP motor 4 Nos what is total load of plant if one of each is stand by.
WHAT IS REMOTE CONTROLLED DG? WHAT IS DIFFERENCE BETWEEN REMOTE CONTROLLED DG & NORMAL DG SETS
which winding aply in an alternator?
why we use ac?why we use dc? why we we cannot use only ac/dc for all the applications?what happen if we use?
IS it possible for a feedbacksurge to travel over a wireless connection?
how to carry out Magnetizing Current Test on Distribution transformer and what purpose we are doing this test.
how to check dc current,how to fix ammeter in dc line
difference b/w semiconductor and insulator
A.V.R maintains the voltage of a generator when it is in island mode but when the generator is synchronised with grid it maintenance the P.F,how it happens please any body explain it in detail.
what is the mazor difference between the induction transformer and synchonous motor?what is the similarity between them?
what is diversity factor ? plzzzzzz describe me