What is the function of an Auto reclosure relay. How does it
work??
Answers were Sorted based on User's Feedback
Answer / varun
It can be expalined by example: in rainy seasons beacuse of
high wind velocity and other disturbances power line can
touch each other . This is recorded as fault by relay (
LG,LLG, etc) and which last for only second. So unnecessary
tripping will be there, so autoreclosure relay is there
which makes breaker to again on and continuing the supply
| Is This Answer Correct ? | 22 Yes | 0 No |
Answer / k.prakashchandra
It closes the breaker after the set time automatically ,on
tripping.It has a timer switch to give closing command
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / palanisrinivasan
When transient fault occurs in the line Breaker will trip &
re-close automatically with set time.
When permanent fault occurs in line the breaker will trip
and auto re-closer will block.
| Is This Answer Correct ? | 6 Yes | 0 No |
If single phase fault (any one particular phase to ground fault) exist in the transmission line AR will operate. But single phase fault should be in zone-1 of the protected line. Then only AR will perform. If fault is in transient in nature then particular line breaker will open and wait for dead time after that breaker will reclaim if fault is cleared then no problem other wise differential relay will initiate three pole trip. This AR is mainly to minimize the outages.
| Is This Answer Correct ? | 1 Yes | 0 No |
I completed my BE EEE degree 2006 .... which license should i apply .... ?????
WITCH CARDS IN USE IN FIRE CONTROL PANEL.
What does Bode plot tell you?
Why is it not possible to operate a star-delta transformer in parallel with delta-delta transformer?
What are the types of AMF(auto main failure) panel.
my first school?
What is the principle of Excitation.
how to deside the capacity of chock for drive?
in 132kv substation CRT means
why odd hormonics only will effect the power system.why not even hormonics
v=I*R, i.e V is directly proportional to I. now P=V*I. so V=P/I. thus v is inversely proportional to I. so what is the correct one? If both are correct than for which kind of condition this 2 differ
How can transformer winding insulation be measured (Delta & Star Connections)?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)