How open delta used for protection?
Answers were Sorted based on User's Feedback
Answer / madhu
the neutral grounding transformer is star connected on the
primary and has an open delta on it's secondary.Open Delta
has two terminals.A resistor is conected across these two
terminals. whenever a fault occurs, an emf will be induced
in the open delta and there will be a voltage drop in the
resistor connected. this voltage drop will be sensed by the
potential transformer connected across this resistor. at
the secondary of the potential transformer we have the
neutral displacement relay which will give a trip signal or
an alarm whenever its settings exceed a particular value.
| Is This Answer Correct ? | 46 Yes | 4 No |
Answer / gunasekaran
at balance condition voltage appear across the open delta
connection is zero at fault candition no longer zero.
so we r using this open delta connection for resudial over
voltage protection.
| Is This Answer Correct ? | 23 Yes | 0 No |
Answer / k.prakashchandra
This relay is used for stator earth fault protection for
generators.The vector sum of three phases in all corners of
delta connected PT secondaries is zero.One of the corners is
taken through a voltage relay.Operation is as above.
| Is This Answer Correct ? | 9 Yes | 1 No |
what is work of choke in tube light?
What is minimum permicible value of leackage current for LT Panle when applying voltage up to 3 KV for 5 Minuits?
what is the formula for calculating motor rating? Example: If we want to rotate a 1000 kg waight disc up to 100 RPM, which size motor will require?
what is formula of illumation calculation
you are a electrical student, why are you coming for software job.
how much air gap in induction motor as per the Indian standards?
A distribution transformer giving afrequency of 200HZ, where it is rated for 50HZ. when it will occure?
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
how can we calculate fault current of a line in a 6 bus syatem if the faulted line is known?
state working of halogen lamp?
how will calculate the safe starting current of 3-phase squirrel cage induction motor?
What is the difference between Neutral and Eatrh?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)