For Eg a 30 kw motor at full load how much kw it takes And
at no load how much KW it will take?
Answer / ahamad kutty k.v.
If an efficiency of 90% is assumed the motor can take 33kw
input to deliver a 30kw load and at no load the losses must
be less than 5% ie: it will take less than 1.5kw.
Is This Answer Correct ? | 0 Yes | 1 No |
Will sag depends on the Specific Resistance of the conductor?if not Why??????????
How to select a cable size according to load
what is the voltage of insulation megger that should be used for measuring the resitance of 66kv equipments.
Is only insulation the difference between High voltage and Medium voltage cable?
can u name the different types of motors used in different types of applications?
whether energy meter is connected in series or parallel.why?
What is the maximum allowed kwa through 2.5mm cable. Electric company installed 2 electric meter at my premises . Two jumper wires of 2.5 mm are used to connect . 2 single phase meters with allowable load 6 and 3 kwa. These jumper wires are taken from a 3 phase electric meter. Meters are in open Sun. What max load these wires can take.