What will hapen if we run generator below 47.6hz frequency?
Answers were Sorted based on User's Feedback
Answer / manoj sharma
Actually in india our all power system equipments are
designed to operate at 50 HZ. at lower frequency
performance of these component is poor in view of power,
life of equipment and safety. Motors will run slower,
transformers output will reduce, harmonics will increase in
power system. second thing when you run generator at
47.6HZ, your generator will loss its synchronism with the
grid.
Is This Answer Correct ? | 52 Yes | 2 No |
Answer / a.mishra
According to Alternator voltage eqn., MAX.FLUX is inversly
proportional to FREQUENCY. If we reduce the frequency,then
max. flux will increase and the problem of core saturation
may happen. Other problem of iron losses will increase in
that alternator as well as the system equipments connected
to that source like Transformers,induction motors.
Is This Answer Correct ? | 9 Yes | 1 No |
since all the equipments are designed to run at a frequency
of 50 Hz ( +/- 2 Hz) , low freuency will make the generator
to run at a speed less than the designed value thus
hindering the designed value of output.
Is This Answer Correct ? | 8 Yes | 5 No |
Answer / vimal dixit
Generator will go out from synchronizm with grid.
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / piyush maghnani
A sthe generator frq reduced the inductive load will draw
high current which will result in poor power regulation.
the motors will not be running with standard speeds. there
will be increase in harmonics disturbances. your generator
will be overloaded & loose synchronisation with grid supply.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / gunasekaran
turbine blade will be damaged frequency variation in india
only +-3% only.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / vivekanand
Hi, do any legal standard for frequency tolerance
recommendation is there for the diesel fueled genset?
Do special criteria for frequency tolerance based on loading
is mentioned in any legal standard?
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rahul
Nothing will happen because we can operate a frequency + or- 5%.
Is This Answer Correct ? | 0 Yes | 5 No |
Answer / praveen420
In india we can't get power frequency less than 48.5hz.
Below this frequency power system violate.
If we run motor below this range than motor coil will be
burn due to more losses.
Is This Answer Correct ? | 6 Yes | 25 No |
What are the tests to be taken on a transformer and generator?
how we can calculate which capacity capacitor bank we have to add for improve pf?
3 Answers Consultancy, JM Huber, Torrent Power,
How do we find the rating of a transformer, if it got burnt badly.
we have a 2.5hp Starite electric motor water pump,the elec motor burned out,we need to replace starting capacitor(old capacitor specs erased),what microfarad rating capacitor do we need? 110-125V
suppose MCC (Motor control center)panel work on field the relay on this damage or not work and earth fault occurs in this and no indication in relay panel given below. than MCB trip or not and what effect the panel how find relay will damage or not work.
why stator winding of synchronous machine are connected in star connection ?
WHY IS THE EARTH FAULT CURRENT ALWAYS LESS THAN THE NORMAL CURRENT??
why are the a.c.series motors preferred for electric traction
what is wave trap? And how it works?
How to select the earthing transformer,for DELTA TO DELTA TRANSFORMER OR ALTERNATOR SIDE.Pls post your answers and calculation.
prove that inegration of { e^z / z^2 + pi^2 }dz is equal to i/pi by Cauchy Residue Theorem.
Whats the difference between three phase and single phase?