For a Potential Transformer(PT), the primary neutral
terminal must be grounded before energization. Why....?
What will be heppend if we energize the PT without grounded
the primary neutral point? Why..........?
Answers were Sorted based on User's Feedback
while connecting pt each primary phase winding is connected to phase to earth. The neutral point of load is connected to neutral point of secondary’s. Neutral point of primary is solidly earthed.
If primary neutral is not earthed the zero sequence component of voltages (due to earth fault) cannot flow through primary windings. Hence phase to earth voltages of system which contain zero sequence component do not get truly transformed and measured voltage are distorted. Hence the earth fault on system cannot be sensed on secondary side of VT.
Is This Answer Correct ? | 21 Yes | 2 No |
why are we using multiples of 11 in substation.
As you achieve greater success with the company after some years, Will you like to be a share holder in our company?
For RCD (Residual current device) Icu is defined. How i can find Ics for them?
what's the reson that,Load is not same on VFD I/P and O/P Side.whenever DOL condition load is same I/P and O/P side.
what is motor
What is meant by earthhing of a magnetic flow meter and when to use empty pipe detection?
Can anyone tell me some hints about what type of questions are asked by the interviewer by an Electronics engineer when company is installing an IPP and wants a team of engineers?
1.What is the difference between isolators and circuitbreakers? 2.What is bus-bar?
sir i have applied for isro-09. still i did not got the HALL TICKET.
what is the breakdown voltage value in BDV test in transformers?
If we know the load for generator in KW then how it will be change to amps and also if we know the load in amps how it will change in KW and what Generator is good for that...suppose load is 500 amps 3phase......??
what is the earth current,reverse power,electrical trip generator short circuit,low voltage, high voltage please discribe me