Answer / katoch
it should be zero volts.but practicaly when we check
voltage b/w nutral and ground it is found near about 1 to 2
volts
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / rams dharavath
The voltage between neutral and ground should be less than 5volts
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kalidassallinterview
It should be zero. In power plant and substaton thay
maintain less then 1 ohm of earth resistence. So, to reduce
the voltae drop the neutral and body earth shold be perfect.
kd
9840159504
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / k.p.sharma
it should be 55 volts if you keep isolated secondaries
(110v sIDE. REST ANSWERS ARE NOT RELEVENT WITH QYSTION
ASKED.
Is This Answer Correct ? | 0 Yes | 5 No |
What is differential relay? How it operates?
Why Generator rotate only clock wise ?
what is the meaning of rms value
24 Answers Fitter, IOCL, OCL,
how bucchos relay works in a transformer
What is the difference between bundled conductors and double circuit?
What is LOTO?
what is the maximum permissible limit value of leakage current and leakage counter reading to replace lightining arrester?
Is it possible to measure correct value of earth resistance & cable insulation ristance with out disconncting earth lead & both sides of cable ends? If not, any other method to measure ER & CIR with out disconneting from the system.
what is the diffrence between mcb &elcb?
What is surge impedence and surge loading....???
what are the usual topology of transformers at different substations in the power system and why that particular topology is choosen. what are the limitaions of that topology?
800A 22KV TP OCB. explain