how much current does 3ph. 10 hp ac motor draw.
Answers were Sorted based on User's Feedback
Answer / pillay
how much current a 3 ph 10 hp motor takes is depending
on the load it is carrying. Genarally the max
safe current for a motor rated as 10 hp at
440 volts is about 14 amps.If it is consuming less
than 14 amps, that means it is under loaded but if it is
carrying more than 14 amps than IT MEANS IT IS OVERLOADED
which is harmful for the motor.
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / emitparmar
10 Hp Motor....
1 Hp = 746 watts..
so 7460 w is the power drawn by 3-ph motor. and three phase
voltage is 415 voltage.
so I = P/V,
= 7460/415
= 17.97 A
| Is This Answer Correct ? | 5 Yes | 19 No |
Application wise, where we should use AC motors and where we should DC motors?
Explain the experiment on ward leonard method of a speed control on a dc shunt motor with an suitable circuit diagram.
A Question Like A Wire Is Wound Whose Resistance Is Some 132. 44647 Ohms. If A Voltage Of 30 mv, 296 Ma Current Is Applied To It What Is The Resistance.
please give me all the Alarm .Trip ,Safety Relays & Conditions of UPS Systems mail me on ashokbabunhce@gmail.com
Can we parallel two grid with different incoming voltage. Ex.let say one grid is 132kv and another is 220kv.
without any theoretical calculations, can u approximately tell the current rating of a motor(above 30hp)working at 415VAC.
Define step response?
what is mean by kneepoint voltage? when it will happen? ( my doubt is, if CT secondary is open means ct get saturation or blas? what are factors are required for calculations? plz give currect anws:
how can we measure 220kv or more than these voltages ...?and also how can we conform whether we r getting 220kv from generating stations throuth the h v transmission lines?
what is the acceptable insulation resistance for motor/transformer?
2 Answers Reliance, Tata Motors,
If R and Y terminals are short circuited,then power will cut. we all know that power cannot be stored.what will happen to already generated power at power station?
I want to give Power supply to a house from the Feeder, Total Load of the House is 128 KW, how to calculate cable size for this load ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)