Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how much current does 3ph. 10 hp ac motor draw.

Answers were Sorted based on User's Feedback



how much current does 3ph. 10 hp ac motor draw...

Answer / ramesh

1 Hp = 746 watts
10 Hp Motor
10*746=7460w
so 7460 w is the power drawn by 3-ph motor. and three phase
voltage is 415 voltage.

so I = P/root3*v*pf*eff
i=Wattage/1.732*415*0.8*0.85
=7460/1.732*415*0.8*0.85
=7460/489
=15.25A

Is This Answer Correct ?    78 Yes 18 No

how much current does 3ph. 10 hp ac motor draw...

Answer / ramesh herur

The current drawn is Approx 16 Amps

Is This Answer Correct ?    46 Yes 12 No

how much current does 3ph. 10 hp ac motor draw...

Answer / karthik.j

10HP = 10*745watts = 7.45kW
I = 7.45/(1.732*415(volt)*0.8(power factor)*0.8(efficiency)
= 16.19Amps

Is This Answer Correct ?    25 Yes 8 No

how much current does 3ph. 10 hp ac motor draw...

Answer / pillay

how much current a 3 ph 10 hp motor takes is depending
on the load it is carrying. Genarally the max
safe current for a motor rated as 10 hp at
440 volts is about 14 amps.If it is consuming less
than 14 amps, that means it is under loaded but if it is
carrying more than 14 amps than IT MEANS IT IS OVERLOADED
which is harmful for the motor.

Is This Answer Correct ?    12 Yes 5 No

how much current does 3ph. 10 hp ac motor draw...

Answer / thalha

3ph 10HP full load current is 13.5...
load current is taken only how the load is connected..
We use star/delta starter mean running current is low than DOL starter...

Is This Answer Correct ?    10 Yes 10 No

how much current does 3ph. 10 hp ac motor draw...

Answer / keshava c

But eff.0.85 how to take o. 85 efficiency

Is This Answer Correct ?    0 Yes 0 No

how much current does 3ph. 10 hp ac motor draw...

Answer / bala.a

Laod = 10 HP = 10 * 0.746 =7.46 KW
= 7.46 * 1000 / RT 3 * 415= 10.38 A
Consider 1.6 Time for starting current = 10.38 * 1.6 =
16.06 A

Is This Answer Correct ?    10 Yes 14 No

how much current does 3ph. 10 hp ac motor draw...

Answer / emitparmar

10 Hp Motor....
1 Hp = 746 watts..

so 7460 w is the power drawn by 3-ph motor. and three phase
voltage is 415 voltage.

so I = P/V,
= 7460/415
= 17.97 A

Is This Answer Correct ?    5 Yes 19 No

Post New Answer

More Electrical Engineering Interview Questions

WHAT IS THE NECESSITY OF GIVING PARTICULAR COLOURS FOR 3 PHASE TRANSFORMERS.....

5 Answers  


why the voltage level is changed when the unearth cable is earth

2 Answers  


Ratings of power transformer,Distribution transformer.

0 Answers  


explain transformer ct connection?

0 Answers  


what is meant by tranformer impedance?

0 Answers   Synergy,


How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva oil type transformer system? plz provide step by step calculation

15 Answers   Engineers India, Indian Railways, Polycab, Shashwat, Sitara Energy, Sonali Bank,


WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off). Sometimes this MCCB is tripping .But no trip in DB MCB. Can anybody tell me reason ? From where i can know about the MCCB settings?

5 Answers  


what is the purpose of interpose t/f in control and relay ckts?

2 Answers  


what is the difference between effective earthing and resistive earthing?

3 Answers   REL,


the minimum clearance b/w ceiling and plane of leaf of ceilng fan shall be ..........mm

1 Answers  


What is the difference between Relay and Contactor

35 Answers   Siemens,


why the starting torque is high in dc series motor..

3 Answers   GM General Motors,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)