while connecting pt each primary phase winding is connected to phase to earth. The neutral point of load is connected to neutral point of secondary’s. Neutral point of primary is solidly earthed.
If primary neutral is not earthed the zero sequence component of voltages (due to earth fault) cannot flow through primary windings. Hence phase to earth voltages of system which contain zero sequence component do not get truly transformed and measured voltage are distorted. Hence the earth fault on system cannot be sensed on secondary side of VT.
| Is This Answer Correct ? | 22 Yes | 2 No |
Post New Answer View All Answers
What are the advantages of instrument transformer?
What is difference between start imitation and start interlock for 3 phase motor protection ?
what is the correct format to create a resume for interview??
Why do we need interlocking in a HT metering or Ring main unit switchgear?
we have a rewind motor of 2Hp,2800Rpm, 220Volt AC. how can we choose the running capacitor for this motor, any formula for that?
If the line voltage is reduced to 75% of its rated value then by what percentage current will reduce ?? 75% 25% 50% no change and why ?
Connection diagram for KW meter and Kva meter
how a resistor resists to flow the current?how an inductor oppses the sudden change in current?how a capacitor opposes a DC voltage.
The SFC of an engine is 0.25 kg/kW hr. when the fuel used has a calorific value of 36000 kJ/kg. the thermal efficiency of the engine is
what is the illumination level required for child play area?
The sodium vapor lamp is not glows when it is connected a distance of 5 meters above from gearbox, why ?
how to select the no. of brushes in a lap winding?
Graphs of measuring power and speed on dc motor
what is Different between Bilinear and Unilenier?
Is a d.c.compound motor is use as a booster? how?