what happen if i connect DYn11 and DYn1 vector group
transformer in parrallel?other things are same like votage
ration,x/r ratiob etc...
Answers were Sorted based on User's Feedback
Answer / salah
Dyn11-secondary voltage lags primary by 30degree
Dyn1-secondary voltage leads primary by 30deg
hence it is not satisfying the condition for
pare;;alisation .
if we connect two TR in parallel current drwn form the
source by both transformer is not in phase hence
circulating current will produce & damage the winding as
well in secondary aslo
| Is This Answer Correct ? | 38 Yes | 13 No |
Answer / tanesh
When DYn11 and DYn1 are out of phase by 60deg. Although the magnitude of both transformers are same, but phase different would cause potential difference between the transformers. This will cause short circuit the two transformers are paralleled.
| Is This Answer Correct ? | 4 Yes | 3 No |
Doug - you are absolutely right for Dyn1. To look at this graphically, a positive 30 degree angle of secondary to primary means that secondary voltage sinusoidal wave starts 30 degrees after the primary sinusoidal wave. Hence in reality it is indeed lagging the primary. Just reverse for Dyn11.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / doug marshall
As I understand it, the convention is counterclockwise
rotation. Therefore DYn1 means that the secondary lags the
primary by 30 degrees (Subtractive Polarity). DYn11 means
that the secondary lags the primary by 330 degrees which is
the same as secondary leads the primary by 30 degrees
(Additive Polarity). Likewise, a DYn1 when operated as a
YnD1 (Step Up), the secondary or delta leads the primary Y
by 30 degrees. Therefore two DYn1 transformers connected in
series DYn1 - DYn1, the output will lag the input by 60
degrees but YnD1 - DYn1, the first stage results in the
intermediate voltage (Delta) leads by 30 degrees and at the
last stage, there is a 30 degrees lagging phase shift so
the sum phase shift from Y - Y is 0 degrees.
| Is This Answer Correct ? | 7 Yes | 17 No |
Alternator rotor earth fault relay circuit
Why converter duty transformer neutrals are not earthed...i am still not sure if this question is also correct...Please email at ranjan120482@gmail.com
what is called inrush current??
How phase to phase voltage comes 440V.
if there is nutral in phase why we use earthing wire and grounding? even at fault condition the fault current flows to neutral (it is a lower path)
In a Capacitor the electric charge is stored in:
2 Answers TELK Transformers And Electricals Kerala Limited,
What are the different modes of plc processor?
What is means by MacAdam Ellipse?
What is the difference between tie bus and bus coupler?
why EMF IS INDUCED IN A CONDUCTOR WHEN FLUX LINKING WITH IT CHANGES ACCORDING TO FARADAYS LAW.
What is relation bet kvar & microfarad
Why use the VCB at High Transmission System ? Why can't use ACB? Pls explain the ans.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)