How to calculate cable sizes in sq.mm. with using motor KW?
Any formula there?
Answers were Sorted based on User's Feedback
Answer / khalander mulla
normally for copper cable 2.5amps 1sq mm
for alluminium cable 1.5 amps for 1sqmm
| Is This Answer Correct ? | 432 Yes | 143 No |
First of all you need to verified full load current of motor,
How can you calculate:
Ex: 1 Motor - 20HP 3ph. 415V 50Hz, 80% efficiency
Cal: A= HPx746/(sqrt3xVoltxPFxefficiency)
=20x746/1.732x415x0.8x0.8
=32.43Amp.
We all know that a motor has 1.5 times starting current,
Then 32.43x1.5 = 48.65Amp
Now you can see in the current currying capacity of cable from manufacturer cable's list.
3.5 x 35 sqmm xlpe cable is sufficient for full load.
| Is This Answer Correct ? | 347 Yes | 171 No |
Answer / bethi arun reddy
normally for copper cable 2.5amps 1sq mm
for aluminium cable 1.5 amps for 1sq mm
That is the answer.......
| Is This Answer Correct ? | 149 Yes | 77 No |
Answer / abdool
3pahse power is P(in KiloWatt)=I.V.PF.(root 3).....
I=1.74 x P(KW)
EXAMPLE:
so, assume 3ph 400V 15KW motor, In=1.74x15=26.1 A,
& 15KW=20HP.....so 2xIn=Breaker rating= 52.2A
...choose 63A MCB
Cable size normally 20-25% higher than breaker to avoid
cable heat/burn accident in overcurrent fault. so, 1.25xIn=
62.64A so choose 80A Cable rating of 25mm2.
| Is This Answer Correct ? | 101 Yes | 66 No |
Answer / parveen
We must consider numerous factors to calculate the exact
safe size of the cables for a particular load.
Please let us know whether the cable is to be laid in
ground or it will be overhead or any other way.
Secondly, you want an aluminium cable or copper cable?
Thirdly, the load is single phase or 3-phase?
Moreover, the motor is induction motor or any other type?
because we have to consider harmonics also.
For e.g for a 3-phase load of 80kw, the aluminium cable to
be laid inside the ground must be 150 sq.mm for perfectly
safe operation.
| Is This Answer Correct ? | 41 Yes | 14 No |
Answer / a.bala
Hameent your statment is applicable for only small cable
size ( Up to 16 sq mm ) Please reff any one catalouge
| Is This Answer Correct ? | 50 Yes | 32 No |
Answer / rana farrukh anwsr
First of all we will chk rated amp mentioned on motor then will check from chart abt cable sq mom size
| Is This Answer Correct ? | 23 Yes | 9 No |
Answer / ramkashyap
For Cable Current Capacity = 4X Size of Cable in Sq.mm, Ex. For 2.5 Sq.mm = 4×2.5 = 9 Amp.
| Is This Answer Correct ? | 48 Yes | 38 No |
Answer / s d chilatre
required copper wire in kg for rewinding Ind. motor for various rating
| Is This Answer Correct ? | 10 Yes | 3 No |
where we use stardelta starter and dol starter
Define relative stability.
If we have 11 kv RYB Phase single core cable near about. Then wht effect and losses
What is the starting current of a motor?
sir, in a industry present pf is 0.54 pf 25hp power is there its want improve 0.9 pf. which suitable capacity capacitor is suitable please inform me.
How wire size can define in electrical wiring? What is the ratio?
Hai, I am from EEE branch.On feb 17 iam going to write an Exam for hindustan petrolium corporation Ltd.So plz send me the written exam pattern/Q's/interview questions.please mail to yuva_polisetti@yahoo.co.in
How Can Be Size Of Transformer Corelate With Freqvence?
is high voltage or high current is danger
Earth Resistivity
What will happen if 230V DC motor connected to 230V AC Supply?
15 Answers Ashok Leyland, BOC, JSW, ONGC, RRB, TRB,
11kv alternator commissioning test?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)