How to calculate cable sizes in sq.mm. with using motor KW?
Any formula there?

Answers were Sorted based on User's Feedback



How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / khalander mulla

normally for copper cable 2.5amps 1sq mm
for alluminium cable 1.5 amps for 1sqmm

Is This Answer Correct ?    432 Yes 143 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / sagir siddiqui

First of all you need to verified full load current of motor,
How can you calculate:
Ex: 1 Motor - 20HP 3ph. 415V 50Hz, 80% efficiency

Cal: A= HPx746/(sqrt3xVoltxPFxefficiency)

=20x746/1.732x415x0.8x0.8

=32.43Amp.

We all know that a motor has 1.5 times starting current,

Then 32.43x1.5 = 48.65Amp

Now you can see in the current currying capacity of cable from manufacturer cable's list.

3.5 x 35 sqmm xlpe cable is sufficient for full load.

Is This Answer Correct ?    347 Yes 171 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / bethi arun reddy

normally for copper cable 2.5amps 1sq mm
for aluminium cable 1.5 amps for 1sq mm
That is the answer.......

Is This Answer Correct ?    149 Yes 77 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / abdool

3pahse power is P(in KiloWatt)=I.V.PF.(root 3).....
I=1.74 x P(KW)
EXAMPLE:
so, assume 3ph 400V 15KW motor, In=1.74x15=26.1 A,
& 15KW=20HP.....so 2xIn=Breaker rating= 52.2A
...choose 63A MCB

Cable size normally 20-25% higher than breaker to avoid
cable heat/burn accident in overcurrent fault. so, 1.25xIn=
62.64A so choose 80A Cable rating of 25mm2.

Is This Answer Correct ?    101 Yes 66 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / parveen

We must consider numerous factors to calculate the exact
safe size of the cables for a particular load.
Please let us know whether the cable is to be laid in
ground or it will be overhead or any other way.
Secondly, you want an aluminium cable or copper cable?
Thirdly, the load is single phase or 3-phase?
Moreover, the motor is induction motor or any other type?
because we have to consider harmonics also.

For e.g for a 3-phase load of 80kw, the aluminium cable to
be laid inside the ground must be 150 sq.mm for perfectly
safe operation.

Is This Answer Correct ?    41 Yes 14 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / sharma

kw to cable size

Is This Answer Correct ?    37 Yes 11 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / a.bala

Hameent your statment is applicable for only small cable
size ( Up to 16 sq mm ) Please reff any one catalouge

Is This Answer Correct ?    50 Yes 32 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / rana farrukh anwsr

First of all we will chk rated amp mentioned on motor then will check from chart abt cable sq mom size

Is This Answer Correct ?    23 Yes 9 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / ramkashyap

For Cable Current Capacity = 4X Size of Cable in Sq.mm, Ex. For 2.5 Sq.mm = 4×2.5 = 9 Amp.

Is This Answer Correct ?    48 Yes 38 No

How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?..

Answer / s d chilatre

required copper wire in kg for rewinding Ind. motor for various rating

Is This Answer Correct ?    10 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

How halogen & merquery lamp works.

0 Answers  


What is the make of breakers, transformers, generators? What are their capacities and ratings?

1 Answers  


What is electrical diversity factor in electrical installations?

0 Answers  


what is Insulation monitoring device. where it is used? (in switchgear room or control panel or in field equipment)

0 Answers  


how to protect transformer

2 Answers  






why stator winding of synchronous machine are connected in star connection ?

1 Answers  


Difference between ups

32 Answers   Emerson, Tata Power,


why we are called the 4-20ma transducer,not 0-20 ma transducer??

3 Answers  


What is the practical way to calculate the cable size for known ampere load?

0 Answers  


Differance between power circuit and control circuit

3 Answers  


how can i find ct ratio of meter by seeing name plate of meter and how it should be used in MF calculation if it shows only-/1???

0 Answers   Harshal Electrical,


What do you mean by lighting transformer?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)