How to calculate & connection of 900KVA generator
2 sets & load(1500A)?
How to choose cable size and ACB size for this load &
generator?
please explain me detail.
Regards,
Mr.Han
Answers were Sorted based on User's Feedback
Answer / subra
ACB ------- 2500A
cable size = 630sqmm X two per phase one 630 sq mm for N total seven 630sqmm cable need
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / bala_vlsi
U Can select 1600 A breaker for incoming of D.G source
and u can refere cable calouge and select the suitable
cable for 1500A THAT TIME U SHOULD CONSIDER VOTAGE DROP
CALCULATION FOR THE SELECTED CABLE .
| Is This Answer Correct ? | 5 Yes | 3 No |
What is chopper
how much importance of power factor in single phase. is it,s importance is quiet same as like three phase power system.
how much amp MCB is required for 1/2 kva power back up?
Explain the method to keep noises low in a control system?
upto how much low RPM we will run the commercial motor which is run through VFD without any problem occurs in motor.Motor rating Duty is S1 & RPM is 1400.
What is Skin effect of the cable?
kindly send me 11KV MV motor differential protection procedure by primary injection method.
Why we use mostly circular coil in transformer? not square or rectangular type of coil.
In winter we seem lightly an electric shock when we touch to doors(sometime)
How is the connection of the tap changer on the HV side been made?
does magnetic interlocking take place in an induction motor ?
how to check ac servo motor
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)