How to calculate & connection of 900KVA generator
2 sets & load(1500A)?
How to choose cable size and ACB size for this load &
generator?
please explain me detail.
Regards,
Mr.Han
Answers were Sorted based on User's Feedback
Answer / subra
ACB ------- 2500A
cable size = 630sqmm X two per phase one 630 sq mm for N total seven 630sqmm cable need
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / bala_vlsi
U Can select 1600 A breaker for incoming of D.G source
and u can refere cable calouge and select the suitable
cable for 1500A THAT TIME U SHOULD CONSIDER VOTAGE DROP
CALCULATION FOR THE SELECTED CABLE .
Is This Answer Correct ? | 5 Yes | 3 No |
how can we know the size of cable cross-section from current rating ?
how can we Increase the Value Of Frequency in electric circuits
What are the protections to be used for Generator?
What shall be minimum thickness of firewall in between two transformers and which code specifies it ?
why an ac solenoid valve attract the plunger eventhough we interchanges the terminal?will the ploes changes?
UG cable sizes were specified in sqmm. But practically its not coming to mesure. What's the reason for that? And how they specify the size of the cable?
hi frnds...pls send me aptransco previous papers .....pls..pls,,,(madhar.rocking@gmail.com)and suggest me some websites
why should the lowest unit of a testing transformer ( cascaded transformer ) have higher power rating??
If we have 630kva step down transformer to operation 3 phase motor 150 kva which size of cable is used? at circuit breaker to 3 phase motor or to electrical board
In 400KV Switchyard, we have used Circuit Breaker With PIR, what is the significance of PIR & why they'r used?
a 25kvar capacitor bank connected to the secondary side of transformer.then why the capacitor draws more current then rated
suppose a fan is running with phase and neutral. if its neural is touched to body. then fan get stopped. if this fan is connected to phase and ground supply..then why it runs?