How to calculate & connection of 900KVA generator 2 sets & load(1500A)? How to choose cab..

Answer / subra

ACB ------- 2500A
cable size = 630sqmm X two per phase one 630 sq mm for N total seven 630sqmm cable need

Is This Answer Correct ?    4 Yes 1 No

How to calculate & connection of 900KVA generator 2 sets & load(1500A)? How to choose cab..

Answer / bala_vlsi

U Can select 1600 A breaker for incoming of D.G source
and u can refere cable calouge and select the suitable
cable for 1500A THAT TIME U SHOULD CONSIDER VOTAGE DROP
CALCULATION FOR THE SELECTED CABLE .

Is This Answer Correct ?    5 Yes 3 No

How to calculate & connection of 900KVA generator 2 sets & load(1500A)? How to choose cab..

Answer / ganesh

All dg 9oo*1.39a =1251a (415v , pf .8,)
1251*1.5 time full load current 1876 A
you choose 2000A breaker
300*6 sq mm2
or 225*7 SQMM2

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

how can we know the size of cable cross-section from current rating ?

3 Answers  


how can we Increase the Value Of Frequency in electric circuits

0 Answers   HMK,


What are the protections to be used for Generator?

3 Answers  


What shall be minimum thickness of firewall in between two transformers and which code specifies it ?

1 Answers  


why an ac solenoid valve attract the plunger eventhough we interchanges the terminal?will the ploes changes?

1 Answers  






UG cable sizes were specified in sqmm. But practically its not coming to mesure. What's the reason for that? And how they specify the size of the cable?

0 Answers  


hi frnds...pls send me aptransco previous papers .....pls..pls,,,(madhar.rocking@gmail.com)and suggest me some websites

0 Answers  


why should the lowest unit of a testing transformer ( cascaded transformer ) have higher power rating??

0 Answers   TCS,


If we have 630kva step down transformer to operation 3 phase motor 150 kva which size of cable is used? at circuit breaker to 3 phase motor or to electrical board

1 Answers  


In 400KV Switchyard, we have used Circuit Breaker With PIR, what is the significance of PIR & why they'r used?

2 Answers  


a 25kvar capacitor bank connected to the secondary side of transformer.then why the capacitor draws more current then rated

3 Answers   TATA,


suppose a fan is running with phase and neutral. if its neural is touched to body. then fan get stopped. if this fan is connected to phase and ground supply..then why it runs?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)