why buchholz relay installed in inclined position
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
So that air or gas bubbles enter the chamber of the relay or
in other words,to trap the gas
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / madhusmita
sir prakashchandra plz give detail of ur ans
| Is This Answer Correct ? | 0 Yes | 0 No |
Buchholz relay is installed in inclined position because of its function as it is used for internal fault protection inside the transformer as in case of over heating and loading of transformer oil temperature also increases hence oil expands inside the body of transformer so that excessive oil expands during heating or time of fault enters in buchholz relays body and after a particular level relays coil get trips and gives an alarm to the operator regarding the fault.
| Is This Answer Correct ? | 3 Yes | 3 No |
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The slip when motor stalls is A 1 B 0 C 13.33% D 10.33%
is tree is a good conductor and it may be used for conductor?
Why do you get a typical sound when the transformer is put into operation?
how do we calculate contactor and fuse rating for a motor if its full load current is known,i want exact calculation for 1.5 kw motor????
1 Answers Allied Group, Nucon,
How many earthing pits are requier to disapper the surge current of one lighting arrester.
If the feeder rating is 7.5 kw or 10 HP star-delta feeder, MCCB is taken as 63 a, contactors-32 a, how much will be the OLR rating or which range OLR should be considered when we concern about type-2 coordination?
what types of load we get from the national grid? is this capacitive or inductive?
Find the octal equivalent for the binary number 101101110
plz tell me about for how many rating (for 500kva)how much current taken?
what is the saturation point of crgo lamination.
how do i work out the Amps of a incommer if i am running 1 37 KW motor and a 0,75 KW motor and some solinoids
In a 3 phase,400v,4 wire system, 2 incandescent lamps, one having 230v,100w and the other 230v,200w are connected between r phase- neutral and y phase-neutral respectively. If neutral wire breaks which lamp will fuse first and why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)