Hoe to calculate body earthing conductor size ?
Answer / aamod tripathi
The body earthing conductor sizing is done in india and
internationally by IEEE 80 :2000 standard and IS code 3043
These instruct the different formulae which are to be used
for calculation purpose generally it requires
1. fault current
2. time duration of the fault
3. a factor which is denoted by K and is dependent on the
material used for earthing.Table (1.D)(This takes into
account the ambient and operating temperature of the
material)
In case of a power house where many Transformers and the
switch gears are installed there we have to install
acompletee earthing grid which is like a square or
rectangular net of rods. the number of rods and ground rods.
The most important point in both the powerhouse earthing or
any other kind of earthing we have to keep in mind that the
earthing arrangement should have the resistance less than 1
ohm........ it is an essential conditon that must be
fulfilled.....
| Is This Answer Correct ? | 14 Yes | 5 No |
can I improve the furnace power factor (10 mva transformer) by adding a capacitor bank before the transformer.Does system power factor vary a lot with the furnace PF?
I have a 600VA UPS for computer only. It holds for 20minutes only. 1. Can it be upgraded for longer period.? 2. Can it be used for one ceiling fan and a tube light? If yes, how to upgrade?
what is the harmonics? which harmonics(fundamental and reference) is suitable for calculating capacitor bank and Active filter and passive filter? what is the 1st 2nd 3rd 4th 5th harmonics and effects?
condider as 100 w lamps glowing . for completing a one unit how much time it should glow
what is RR number Abbreviation energy meter
if we give connection of 100watts bulb through a single phase energy meter ,the disc of a meter rotates why it happens?
what is mean by xlpe cables?
why are transformer rating in MVA
What is the voltage violating limit to be considered for load flow study? What is acceptable deviation limit according to relevant standards?
Please give me a ansver for why currant transforme noe point should erthing
What are the maximum and minimum ratings of MCB,MCCB,ACB,OCB,VCB and SF6 breakers?
2 Answers ABB, SK E&C, Sodexo,
hi... Can anybody give me description of type-2 coordination, IP protection, NEMA standards ? Thanks..
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)