how to calculate of which rating transformer should be
selected? take any example
Answers were Sorted based on User's Feedback
Answer / yogesh
Calculate the system connected load.(CL)
Rating of Transformer = (CL*U.F.*M.F.)/(Tran.Effi.*p.f.)
Then consider the loading factor as 80%
as U.F. -Utilisation fsctor & M.F.- Maintenance factor
| Is This Answer Correct ? | 2 Yes | 0 No |
usually transformer rating is based on power to be drawn by
the transformer. however few factor is also play a part
like LF, DF...
For Ex say total Connected load is 820 KW
Maximum Demand would be MD= Total connected Load x L.F (0.8)
xD.F (0.7) = 820 x 0.8 x 0.7 = 459 KW
now considering the load at 0.8 leg PF the kva rating of
the transformer is
KVA required = 459 / 0.8 = 574 Kva say .......600 KVA
| Is This Answer Correct ? | 2 Yes | 0 No |
How you calculating the 30 Hp 3 phase AC motor of power what size of cable is used for this motor?
What are the disadvantages if neutral current exists in grounded star transformer distribution system?
Why P.F(power factor)relay should not be connected to the D.G(diesel generator) incomer side
We store the d.c supply...then why can't we store A.c supply???
my N-P 230 VAC at 3 wires but i haven't any voltages at phase to phase whither my supply is 3 phase, why i haven't received these line to line voltages ?
FACP Means
Hello, im taking an introduction to PLC..and i'm having a hard time on creating a program for 2 lamps blinking alternately with this button characteristics: 1.) One push button (starts upon pressing) 2.) Same push button (when pressed again, will pause the system) 3.) Same push button (when pressed again, will continue the paused system) 4.) Same push button (when pressed within 2 seconds, will shut off the system) Pls..i know this is just a simple problem for you guys..
what is meant by Is limiter?what is the use of current limiters in electrical ditribution network?
can the measured percentage error during calibration of single phase energy meter be negative?
how to calculate optimum loading for transformer?
How to check the cable fault / hv test of transformer cable.
2 v/500amp/hr to 1.80vpc at 20 degree celsious 2v/5ooamp/hr to 1.75 vpc at 77degree farren .this is the capacity of a battery .what is the meaning of this . can i get a detailed explenation
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)