how to calculate of which rating transformer should be
selected? take any example
Answers were Sorted based on User's Feedback
Answer / yogesh
Calculate the system connected load.(CL)
Rating of Transformer = (CL*U.F.*M.F.)/(Tran.Effi.*p.f.)
Then consider the loading factor as 80%
as U.F. -Utilisation fsctor & M.F.- Maintenance factor
Is This Answer Correct ? | 2 Yes | 0 No |
usually transformer rating is based on power to be drawn by
the transformer. however few factor is also play a part
like LF, DF...
For Ex say total Connected load is 820 KW
Maximum Demand would be MD= Total connected Load x L.F (0.8)
xD.F (0.7) = 820 x 0.8 x 0.7 = 459 KW
now considering the load at 0.8 leg PF the kva rating of
the transformer is
KVA required = 459 / 0.8 = 574 Kva say .......600 KVA
Is This Answer Correct ? | 2 Yes | 0 No |
why measure the gravity in battery?
Describe the test procedure to determine the vector group
Can the output voltage of a rectifier be greater than the input AC voltage without the use of any voltage multiplier in the circuit??please provide the explanation too..
i want bhel placement paper for electrical if anybody having pl send to my id kavitha867@myway.com immediately
Pls explan the OLR setting in VCB at HT yard
What is Earth Fault and Over current Fault.
How the annunciator works ? How to do its wiring
Can double compression glands be used with regular cables?
all 3 current transformers (C.T) are burnt in a L.T Panel - what are the possible reasons
which motor have relatively high power factor and what is reason for have high pf? 1.capacitor run motor 2.shaded pole motor 3.capacitor start motor 4.split phase motor
what is mean by derating factor?
What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.