Rated moter voltage and frequency is 380volt 60 hz but moter is running at 380votac 50hz is this harmful for moter winding
Answer / ll.krishna rao
V=4.44fNBA Therefore V is proportional to frequency if you want not to exceed the design parameter of flux density.If you operate a motor at 50Hz instead of its rated 60 Hz,then you will be exceeding the flux density by 120% for 380 v
operation.I suggest you to operate the motor at 380/1.2 volts instead at the expense of full power.
| Is This Answer Correct ? | 2 Yes | 0 No |
why earthing point in the 6amps/16amps socket bigger than the remaining (Phase & Neutral)points.
how to calculate the no. of earth pits required for an electrical installation?
How can step up and step down process in power transformer
1 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
Why does curving the pole faces in a dc machine contributes to a smoother dc output voltage from it?
which calss ct's,pt', use protection,meatering and others
what is mcb
How many types oil using in transformer ? How many letars using in transformer..?
Different types of relay fault which phase sequence??
what is the significance of KV & MVA rating of the transformer and how they are related.
what is the function of AVR in generator? how the generator maintain the frequency while varies the load?
1 KVAR = 1.3Amps but, 25KVAR capacitor/690V capacitor takes just 21Amps as leading current, what is the reason? Please explain...
Pls say , how we calculate lux / sq.ft, which formula used for calculation
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)