Rated moter voltage and frequency is 380volt 60 hz but moter is running at 380votac 50hz is this harmful for moter winding



Rated moter voltage and frequency is 380volt 60 hz but moter is running at 380votac 50hz is this har..

Answer / ll.krishna rao

V=4.44fNBA Therefore V is proportional to frequency if you want not to exceed the design parameter of flux density.If you operate a motor at 50Hz instead of its rated 60 Hz,then you will be exceeding the flux density by 120% for 380 v
operation.I suggest you to operate the motor at 380/1.2 volts instead at the expense of full power.

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Differnce between negative Pahse SequenceFunction and unbalance Function?

1 Answers   Atsco, LMW Lakshmi Machine Works Limited,


Do we really need wheels for the transformer

1 Answers  


what is meant by fuzzy logic? what is fuzzification and defuzzification?

5 Answers   MEIL, Power Grid,


What are all the points to be checked while decanting diesel from tanker lorry to HSD YARD

1 Answers   Cisco,


what is Distance protection & how did it work

2 Answers  


what is the differenc between A.C. and D.C, which is more dangerious?

4 Answers  


when the motor was star position that is running ok but when the motor was delta it was tripped? why?

5 Answers   Nimbus, SEL Manufacturing,


What happens if 25 Hz frequency is applied for 400/200,50 Hz single phase Transformer.Will Voltage increase ?

2 Answers   Bhel, Dawlance, IBM,


what is the difference between relay, contactor

4 Answers   BRSS, Vishay Intertechnology,


1 “earthing” for bonding of equipment and circuits to common plant earth electrode potential, 2 “protective earthing (PE)” when this bonding is required for personal safety provisions 3 “grounding” for interference suppressing bonding of screens, sys-tems with ground level 4. low-impedance earthing ? 5.primary earthing system and secondary earthing system what is that? 6.earthing electrode or mesh net earthing electrode ? very confusing , simple but very informative help required ? i will be very very thankful to you guys.

1 Answers   ABC,


How many size of cable required for a 300m long and 30kw inductive lode

1 Answers  


What is the function of pulse transformer?

4 Answers   Electrotherm,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)