WHAT IS THE DIFFERNCE BETWEEN AIS AND GIS IN SWITCH GEAR?
Answers were Sorted based on User's Feedback
Answer / aamod tripathi
IN GIS SF6 GAS IS USED FOR INSULATION.SINCE SF6 HAS HIGH
DIELECTRIC STRENGTH THAN AIR. AND THUS GIS IS USED FOR
HIGHER VOLTAGES AND REQUIRES MUCH LESS SPACE THEN AIS BUT
AT HIGHER COST.
| Is This Answer Correct ? | 45 Yes | 2 No |
Answer / a.yougaraj
AIS: AIR INSULATED SW. GR.
GIS: GAS INSULATED SW. GR.
| Is This Answer Correct ? | 35 Yes | 7 No |
Answer / eswari
GIS - Gas insulated substation
AIS - Air Inuslated Substation
GIS - high efficiency, requires less maintenance, less
space and less global warming when compared to AIS. but GIS
cost is two times higher than AIS.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / janardhan reddy
IDENTIFICATION OF ERRORS IN GIS IS IS DIFFICULT AND IT WILL TAKE MORE TIME WHEN COMPARED TO AIS
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / jaideep
gis meanse
gas insulated substation
ais means air insulated substation
gis is of high cost than ais
but works efficiently
gis requres very less land when compared with ais
these are some differences there are many
but gis replaces ais in soon
| Is This Answer Correct ? | 15 Yes | 9 No |
what is accuracy ? in any meters , coils accuracy . how can u defined that ?
how to cal calculate capacitance in DC Circuit
1. alternator has full load regulation of 4% when pf of the load is 0.8 lag, 1500 rpm. full load regulation of 1400 rpm for 0.8lag will be ________ ?? 2. torque angle of a sync m/c operating from a constt voltage bus is usually defined as space angle between _______ . 3. method most effective in finding out no load losses in large DC shunt motoris ______ . 4. current carrying capacity of fuse material depends on ______ . 5. coil has res. 10 ohm, inductance 1H. what wil be current after 0.1sec after switching on to a 500V DC SUPPL ? ? 6. effect of phase lag compensation on servo systems ___________ . 7. rotor of a dc machine is usually supported upon ______ . 8. DC motor is preferred to AC motor in which application ?? 9. 3 nos of 10:1 Xmer are connected in Star-Delta to supply a load at 230V.the supply voltage must be ______ . 10. voltage source produces max current in which circuit. 11. cal. power, if current and voltage are out of phase by 90 degree. 12. suitable length of Xmission line of power at 66 KV. 13. Which of the theorm helps in simple computation when the load across a ckt is varying ?? 14. what is the adopted line length for power Xmission of power by cables ??
What shall be the minimum distance to be maintained between two power cable in a common trench?
What is power factor?How to improve power factor
what is REF relay?
How to increase solar cell efficiency ?
One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?
What Is Transformer Impedance ?
why is power supplied in 3 phase only? why not in 2 or 4 phases?
What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?
define electrical field?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)