WHAT ARE THE DATAS REQUIRED FOR SCS SIGNAL LIST PREPARATION?
It depends on your SUB STATION CONTROL SYSTEM (SCS)
supplier and client, and load despatching authority SCADA
system.
Generally Load despatching authority demand:
I) Remote control -on-off control oF CB,STATUS OF
INDICATION,PROTECTION AL+TRIP SIGNALS ,FEED BACK SIGNAL.
OLTC COUNTER,
2) INDICATION - A,V,F,PF, MW,MVAR,
3) METERING IN -OUT MWH,MVARH,
4) sTATUS OF ALL CB,DS,ES, PLC,
5) MAIN BUS ,INCOMMING,OUT GOING.
6)SUB STATION dc VOLTAGE, UPS ALARM
7)FAULT LOGGER REPEATITION SIGNAL.
THIS IS A VERY EXPENSIVE TASK. SCS SUPPLIER MUST FINALIZE
CLEARLY,AFTER FINALIZING SIGNAL SUCH ,AS DI,DO,AI,AO ,LOGIC
SEQUENCES, SHALL PROCEED HIS WORK.
tARIFF METERS ARE VERY EXPENSIVE. SCS MUST FOLLOW LOAD
DESPATCHING REGULATION AND ITS SPECIFICATION.
Is This Answer Correct ? | 1 Yes | 0 No |
What is the meaning of EDO in DG panels?
Advantage of 11KV ring main system with open point
1 Answers Alam Group of Companies,
How the FM200 Gas Supression System wil Work????
How to calculated capacitor rating both HT
What is encoder, how it function
What is the male and female contactors.where is it's used and what is the deferent betweens
Explain role of Buckolz Relay in Transformer ?
What is a signal flow graph?
HOW TO CALCULATE THE VT SIZING?
how can synchronous generator can be used as synchronous condenser?
what is field flash
why we used ZNO in Lightning arrester.