Answer / mahesh sali
mostly total electrical cal.in KW at 0.8 pf as per thumb
rule.
KVA = KW/PF
as per nec code norms ur dg set shall be suitable to take
the higher inrush current during starting.
so awalys keep some say 115% to 125 % on induction motor
load.
for ups & lighting system around 200 to 300 %
Toatl kw rating = 1.25 * Kw ( Plant load )
KVA at 0.8 pf = Total kw/0.8
Assume that Dg set loading at 70%
i.e rated KVA = KVA /0.7
adding some 20% future load
i.e. actual DG ser rating in KVA = rated KVA + rated KVA *
20%
Thanks
| Is This Answer Correct ? | 1 Yes | 0 No |
why does voltage generation at 11 kv?
define power quality
why after termination of HT cable armoured earth connected one end, why not connect other end.pls tell me correct answer.
without name plate detail of blower how we can find out the HP & Rpm ? the input voltage is 230v single phase
what is the spdt
what is the fuction of electrical transducer in control pannel?
whit is 33kv power 300*300 cable full current with formula
what is kVA
1.dg on load alarm/stop alarm... 2.dg on load. piu alarm alarm kaise chek krte hai
what is mean by amf
What is the differance between 2 dc motors of armature voltage 660 v and 440 v?
How will polarity test of Dy5 transformer ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)