What is difference between metal clad & metal enclosed
switchgear?
Answers were Sorted based on User's Feedback
Answer / karunakar
Metal-Clad Switchgear is an assembly of units characterized
by the following features:
The main interrupting device is removable and arranged with
a mechanism for moving it
physically between connected and disconnected positions. It
is equipped with self-aligning and
self-coupling primary and secondary disconnecting devices.
The interrupting devices, buses, voltage transformers, and
control power transformers, are
completely enclosed by grounded metal barriers, which have
no intentional openings between
compartments. A metal barrier in front of the interrupting
device ensures that when, in the
connecting position, no live parts are exposed by the
opening of an enclosure door.
All live parts are enclosed within grounded metal
compartments.
The Metal eclosed switchgear assembly consists of multiple
metal-enclosed, vertical sections. Normally the end
sections are designed to allow for installation of future
sections. Each vertical section consists of up to four
individually enclosed breaker or auxiliary compartments.
Compartments are sized to provide uniform height of each
switchgear assembly.
Various components such as circuit breakers,
instrumentation and control equipment, transformers,
relays, three-phase bus work, all internal wiring,
connectors, and other supporting equipment are included in
each assembly. These units can be directly coupled to 480V
motor control centers if desired
Is This Answer Correct ? | 21 Yes | 5 No |
Answer / gurumurthy.k
The Simple reply is " A metal clad can be a metal enclosed
but a metal enclosed can not be metal clad". Which
means , the Metal enclosed need not have a compartments
within its structure, can have fixed interupting medium and
and safety related issues. These are applicable for a low
coltage swicth board but metal clad is more apt for medium
coltage.
Is This Answer Correct ? | 15 Yes | 2 No |
how to fit 3 HP crompton gear motor with conveyor with the use of staring delta starter or ordinary starter?
When will you multiply and devide with derating factors to the actual value while sizing the cable?
what is the method to calculate the voltage drop for number of meters Example 250volts I/p at one end if the cable length is 50 meters what could be the drop?, after 100 meters how much? needs formulae.
what is the difference between single ratio, multiple core and multiple ratio, multiple core ? please explain.
1ampear me kitna watts hota hai aur elcb ka pura naam kya hai
18 Answers Al Khayyat, Alpha G, BEC, Bhel, CGS, Electrical, Fiem, Firmenich, HLG Habtoor Leighton Group, Jash, Kandia, Maruti Suzuki, Minda, NTPC, ONEIC, Pace Process Controls, SMTC, SR, Sunrise Electrical, Sushil Enterprises, Suzlon, Voltage,
why transmission voltages are in multiple of 11kv?
Why the dc voltage drop during starting of emergency lube oil pump? The Voltage drop from 135kv to 125 kv for one min. before re-establish to 135kv?
WHAT IS THE DIFFERNCE BETWEEN AIS AND GIS IN SWITCH GEAR?
How to check maintenance free battery 12V,26AH using analog multimeter
why the capacitors works on ac only
I AM COMPLETED DIPLOMA IN E.E.E. AS WELL AS B.TECH IN ANDHARPRADESH.. HOW I THE Certificate of competency as Electrical Supervisor.
Technical specification of a wind farm