What is the Different b\w Circuit Breaker & Isolater
Answer Posted / e venkat reddy
CIRCUIT BREAKER WORKS ON ON LOAD WHERE AS ISOLATOR WORKS ON
OFF LOAD CONDITIONS. ISOLATOR WILL OPERATE AFTER THE
CIRCUIT BREAKER ACTION TAKING PLACE.
| Is This Answer Correct ? | 21 Yes | 1 No |
Post New Answer View All Answers
describe the constructional features of an auto transformer and its principle operation
how to select battery for 15 KVA UPS with formula
Why using synchronising methed in DG's sets?
Where should the lighting arrestor be placed in distribution lines?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
what is thermal resistance of PVC Cable.
What are the Full Forms of TVM, MTL, CVT ?
Do you know what is dry-out test in x'mer
what is inverter and converter
Which type of DG need Netral Earthing?
what is high - pot test. what's its use?????
why 5kW motor becomes unbalance if its relay trip 1st time and its set value is 7.0 A
sir plz send some previous year questions of jspl.
the site measured knee point voltage of protection class CTs should be greater than rated knee point voltage? what about meetering class CTs. Should it be below the rated knee point voltage?
working principles of cf lamp,incandescentlamp and f lamp?