why we commonly use delta star winding in power and
distribution transformers
Answer Posted / pankaj malhotra
The best way to minimise 3rd harmonics in the transformers
there are two ways. Either transformermer has low flux
density which is not economical and not in use or to make
atleast one winding of the transformer in delta because 3rd
harmonics are absent in delta. Since the requirement of
three phase four wire system in distribution, we commonly
use delta star winding
| Is This Answer Correct ? | 25 Yes | 3 No |
Post New Answer View All Answers
what is the IPC ? & what the uses ?
1.what is the reason for transformer and lightning arrester blast in 33kv system
What is the polarization index value ? (Pi value)and simple definition of polarization index ?
why you don not show protection and type of isolation in key single line diagram?
What is the maximum operating temperature for a thermoplastic insulated cable?
State kirchoff current law?
What is the rotor frequency of 10 Hp 1440 RPM 50HZ 415V ?
formula for calculation of switchgears(i.e. contactor, fuse, cb, relay etc.), if load current is given?
What is the method to solve circuit using source transformation?
What is core CT & it's function?
What are the factors influence the choice of an electrc drive?
what is the purpose that we use PLC system in power system
There is air in a room . the top and bottom of the room are at constant temp. T1 and T2. DRAW THE temp profiles if a. T1 greater than T2 b. T1 less than T2
if there is nutral in phase why we use earthing wire and grounding? even at fault condition the fault current flows to neutral (it is a lower path)
What do you mean by phasors?