when the operation engineer told you that he gives the
control valve order to open but there is no response !
what will you do ?
and if you found that there is astuck , what will you do ?
(note : it is apanumatic valve )
Answers were Sorted based on User's Feedback
Answer / chitturi bhaskara rao
1.First measure 4-20mA in field side if cannot get 4-20
then check AO card , if u got 4-20 in field side then check
positioner ,
2. make sure thatt sufficent air supply i,e 3 to 4 bar at
inlet of positinoer.
3.If all correct still valve nvr moves then remove
positionner from the valve and supply the air directly to
actuator ( to 4 bar max) then valve moves smoothly then
check angle of postioner while ur fixing positoner on
control valve .
4 if valve nvr moves smoothly means in side valve jam need
to send over haul
| Is This Answer Correct ? | 20 Yes | 0 No |
Answer / maneesh
after doing all the priliminary inspection if u found the
valve is struck, u can directly give the air supply to the
actuator not:direct applying og air supply may diamage the
valve it should be done with sufficiant care.if the struck
is minor by repeaded giving of supply air will slowly
remove the struck.agfer this still its struck u can remove
the valve from the praocess line and chel the valve body
whether any solid material bloks the way.if that u can
clean and fix it back
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / b.kumaran
after doing all the priliminary inspection if u found the
valve is struck, u can directly give the air supply to the
actuator in a repeated manner.if the struck
is minor by repeaded giving of supply air will slowly
remove the struck.still its struck then loosen the body
bolts and try to open by the above method. If still there is
a struck up then u can remove the valve from the process
line, dismantle and clean the valve body whether any solid
material bloks the way.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / 808
Simulate 4-20mA it with a DMM at control valve. If it works
there, then check wiring.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / aatif alvi
check if the proper volatage i.e 4-20ma is changing the the
operation engineer changes he valve position. if it is
changing the the problems might be with the solonoid..some
times moving the solinoid with screw driver makes it work
again,, as it got stuck due to rusting.
| Is This Answer Correct ? | 1 Yes | 4 No |
i have calibrate rosemount make level transmitter , wht can i do ? my tank capacity is 30,000 liter
i have a dp tx range is 5000mmwc. in which calibration i use in a open tank.1.5*3.5*2.5 mtr.for level msmnt. what is the calculation.
if conical type tank in top LEFT side solid material coming but LT MOUNTED IN TOP OF LEFT SIDE, how to measure ultrasonic level transmitter ?
What for barriers are used in DCS & PLC systems?
cheapest instru-- PMMC, EDM, rectifier, thermocouple.
What does a hookup diagram look like? can you give sample drawing. thanks.
what is bms?
give me all the details about the interview and which type of question being asked
what should be the attitude while answering an interviewer?
I will attend an interview with GasGas company for a position of Instrument Technician ( Offshore )in next month can anyone tell me what questions they will ask. Thanks in advance.
what is easiest way to read STL language in PLC?
Why mmwc unit is used?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)