what the differant between Wet Leg /Dry Leg
Answers were Sorted based on User's Feedback
Answer / www.islamqa.com
They are diffrential pressure transmitter "installation
technique" used in "level measurement"
When installing diffrential pressure transmitter we attach 2
impulse lines with high & low transmitter sides, the 1
attached to low side is empty impulse line so it is "dry
leg" or it's filled with a sealing liquid with density
greater than the process liquid so it is "wet leg".
We use "dry leg" for closed pressurized tank.
We use "wet leg" for closed pressurized tank also but if we
have the probability of process liquid condensable vapor
which will give a faulty measurement.
If we have an open tank, the Tx low side is atmospheric.
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
CELL.: 00 2 0121367310
ahmedsabry.onine@gmail.com
| Is This Answer Correct ? | 33 Yes | 0 No |
Answer / heri santoso
Dry and Wet leg are process connection of dp cell level
instrument used in close tank
(Wet leg)Where leg impulse connection of tx contained fill
(difference SG)with process fluid in tank.fill is a
parameter reading of tx tranduser
(Dry leg)where leg impulse connected to atm no fluid in leg
connection
Thanks
| Is This Answer Correct ? | 3 Yes | 11 No |
in DCS or PLC we can not put all ai or di,there is calculation through which we can accomodate certain no of digital and analog signal.I need to know that calculation
Why Pressure Transmitter is NOT installed before up-stream of an ORIFICE PLATE? in a flow measurement.
Whether the DP transmitter can be utilised in the medium of Vaccum for the measurement of Level?
Why we use 4 - 20 ma?
what is metal of piston ring
How does a redundant controller comes in line when the main controller fails??
in the construction field why hook up s.s.tubing for transmitter using upto 6mtrs of closed loop, but y not open loop nomore restriction
Explain PID controller tuning & any one method used for it.
1. what is 3 point calibration & 5 point calibration? 2. If we use hart communicator to set the LRV & URV of a smart transmitter, did we calibrate the transmitter? why? 3. Make a complet list if meterials needed to properly connect a pressure gauge to a steam pipe using 1/2 inch stainless steel tubing. The gauge connections is 1/2 inch NPT-M and the steam pipe tap has a 1/2 inch female coupling, compression fittings are use. 4. What are the tools in loop checking? 5. What would the ISA symbol of a square root extractor look like? 6. What would you do to completely prepare for the configuration? 7. What safety measures must you undertake when doing configuration? 8. what are the two most commonly use programming languages used when we configure a PLC? 9. What would you do if you accidentally skipped a step in the configuration procedure? 10. How would you know if the configuration were sucessful? 11. Name at least 3 selections available when we configure the burnout protection of a controller?
3 Answers EI Electrotechnical Institute,
how to check control valve was passing?how to check online?
calibration of instruments.
what is full form of NAK?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)