Which ciass CT can be use in diff. protection. Can be use
5p20?
Answers were Sorted based on User's Feedback
Conventionally only PS class CT shall be used for unit
protections. But now a days, with the use of miro processor
based relays having facility of low impedance or biased
differential protection, 5P20 may be used as biasing in the
relay takes care of the unmatched characteristics of the
both side Cts.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / avdhesh
Class 5p20 CT is a protection class CT which is used for
normal protections. For differential protection you must
use class PS CT.
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / persistence
yes 5P20 class CT can be used for differential
protection,In our industry they have been used for
transformer differential protection,transformer being 10 mva
and for bus differential protn. class PS has been used.
| Is This Answer Correct ? | 10 Yes | 5 No |
Answer / dharmaraj
For diff.protn you must use ps(or) px class CT.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / dheena hitech
For diff protection we should be use PS or PX class Because
of yjat one ine is spl. class for diff and Dist protection
| Is This Answer Correct ? | 1 Yes | 2 No |
what is the pi test for current transformer?
why middle phase should used for earth fault and other phases used for over current in overcurrent and earth fault relay?
types of motors suitable for escalators with reason
What voltage is used in Directional earth fault relay? and why?
I have c license but I don't know eligibility of Max Kilo Volts under the electrical licensing board.
why incomer bay is required before transformer bay if there are more than 1 nos. of transformer bay.
what is MEMS and any one of it applications?
Mathemetical Relation Between KWRH and KWH?
How to calibrate or test an LT Air Circuit breaker 440 volts, 35 KA, 800 Amps ?
Greeting to all members, How to calculate spill current when we have different ratio CT and Class for REF(Low Imp) I have 500/1A 5P20 @line side n 400/1A CL.X @ Neutral.
what is counter poise conductors
when we have to use UPF wattmeter and LPF wattmeter? what is the difference between UPF and LPF wattmeter in terms of construction?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)