Why is the earth fault relay connected to the Yellow
Phase?
Answers were Sorted based on User's Feedback
Answer / s.patel
There is no condition like that ,we can connect earth fault relay to any one of the R,Y&B phases ..
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / k.prakashchandra
Earth fault relay is not connected any phase.The balancing
current is made to pass through this relay.In two EFR and
one EFR protection scheme,OCR s are usually provided on R
and B phases ,which makes one assume that the EFR is
provided on Y phase.You can have 3 OCR and 1 EFR protection
scheme also
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / k.prakashchandra
It may be noted that EFR is connected between the star
points formed by S1s and S2s of CT secondaries.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
In my answer No.2 pl read as 2OCR and 1 EFR
| Is This Answer Correct ? | 0 Yes | 0 No |
How to Calculate The Neutral Earth flat design calculation for the Synchronised generator (Gen 1-650Kva, Gen 2-725Kva
The efficiency of a 100kva transformer is 0.98 at full load as well as half load , for this transformer what is the Copper loss at full load ?
when we change tha taps from 1-16 in 100mva tr whether a constant voltage avaliable till it reaches tap 16 or voltage change as per taps change
What is the importance of earthing?
What is the function of electron gun used in crt?
In legging current reactive power is arise but in leading current which power will be arise ? and in this case, is active power more than rated ?
how we can calculate LT side current of transformer
How many electrones need to flow in one second to equivalent to one Ampere.
For the same power rating,which motor is bigger in size,AC or DC?
i have 400/230v transformer and didnt done the neutral eatrhing. i connected one lamp to one phase and neutral to the earth. but the lamp is not glowing. again i connected neutral to earth and repeated the same. then the lamp is glowing. in the first condition i tested with a line tester also, at that time the tesrer is glowing what is happening i dont know can any one help me?
what type of protection and safety req. in the 220kv substaion and area around the substation
Why can't we parallel Voltage transformer secondary circuits?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)