what is the diffrence between mcb &elcb?
Answers were Sorted based on User's Feedback
Answer / pillay
MCB is magnetic or thermal protected over current protection
device. that means if the current flowing through this mcb
exceeds the rating of the mcb it would trip. how fast it
trips depends on how much more than the rated current is
flowing through
ELCB is a device to detect any earth leakage current only.
If the leakage current exceeds the rated current the elcb
would trip off the circuit . The ELCB does not give
protection against overcurrent.
| Is This Answer Correct ? | 12 Yes | 0 No |
MCB - Miniature circuit breaker:- Which helps to avoid over current or fault current enter into the circuit.It protect the circuits by tripping operation.This is available up to 63A.
ELCB - Earth leakage circuit breaker:- Which helps to avoid the running current enter into the earth by means of tripping operation.This is available up to 63A.
ersaravananp@gmail.com
| Is This Answer Correct ? | 9 Yes | 1 No |
why we are giving D.C. supply to field of an alternator, why can't we give the a.C. supply
how to find value of resistance when 1 kw consumption for 10 minutes
What is the difference between grounding & earthing?
What happend if we connect star point to ground of a star connected motor? And what will be effect on system and effeciency of motor?
if we want to convert the two 12 V DC batteries in parallel for UPS ? what would be the result ? which is better for a UPS , connect two batteries in series or connect them in parallel ?
difference between generator and alternator
wats the procedure to calculate no of batteries for ups?
what is ballast
How short circuit MVA(Fault MVA) in a power system calculated for calculating number of earth plates ?
In 3.5X150 Sq.mm cable what does 150 stand for outer dia or inner dia?
what is the string efficiency
Three set (each phase contain 2 cable of 400 mmsq CU XLPE AWA) of single core cables are connected to 11 KV motor of 14 MW & the switch gear supplay is taken from 11kv feeder & this supplay taken from 275 KV substation. Problem is one pair cable(L3- 2 cable ) getting very hot & gland melted and damaged in switch gear side. the other two cable haven't any more hot(ambient temp only & L3 haveing 95- 100 Degree C. The same problem happened in 275 KV substation switch gear side also where the supply taken for 11 kv switch gear. But here L2 phese cable had problem. Why it is happening like this?. The cable having temperature different at different location from gland side inthe case of 11KV feeder of 275 kv substation. why ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)