Answer / vivek sri
A correction to my earlier answer(8)
In case we are to use a 3 phase generator then the total
current of 218.75 has to be equally shared between the 3
phases i.e. Iph=218.75/3=72.9 Amps.
So the genset rating would be again 52.5kVA(1.732*415*72.9).
But in actual as the number of AC's is 20;
18 Ac's get distributed equally (6 on each phase L-N) and
the balance 2 nos will be on one phase each.
So the max current will be 76.58 (18/3*10.94+10.94).
So the 3 phase genset rating would be 55kVA (1.732*415*76.58)
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / avnish sharma
I do agree with Mr. Prakash. but he has not considered pf, safety margin, and Future accommodation.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / girijapati mishra
TOTAL REF LOAD =1.5X20 =30 TR
1 TR = 3.5 KW
Thus , 30 TR = 105 KW
COP (i.e ratio of heat removed vs power input ) for AC
varies from 2.5 to 3 depending on design and other
considerations.
Assuming a COP 2.5 ( lower side)
Power required will be 42 kw (=105/2.5).
Considering power factor 0.8 ( gen assumption for all
caculations) rating of the DG set will be 52.5kva ( =42/0.8)
. A DG set higher than this calculated value to to selected
for this requirement.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / sathish reddy
45 KVA Diesel Genset is requied. Calculation is as follows,
20 * 1.5 = 30
Multiply by the MF 1.4
i.e. 30*1.4 = 42 KVA
As after 40 KVA we have 45 KVA as next higher capacity we
have to go by 45 KVA.
| Is This Answer Correct ? | 25 Yes | 22 No |
Answer / lokesh thota
Actually a 1.5tonn a/c will take 15amp at its maximum level
on 220v supply.so,for 20 such ac's you will need around 300
amps from that you can calculate how much Kva d.g u r need
with according to the vol you r selecting
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / jenifer
"Genset Engineering Calc" Version 1.1 is well designed than 1.0
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / prakash suhane
Total Load in T.R = 20X1.5 =30 T.R
1 T.R = 3.5 kw
for 30 T.R 30 X 3.5 = 105 K.w
any D.G set available more then 105 KVA is suitable for
this application.
| Is This Answer Correct ? | 16 Yes | 17 No |
Answer / jagjeet
Dear vIVEK,
Avinash has given correct answer , Generally pf of the
Dg Set is 0.8 and for calculation we are taking 20 %
Pf of Dg set is ==0.8
Safety Marging = 20 %
Future Expansion =20%
so 1.4*105/0.8=183KVA so you will have to go for 180 KVA
DG Set.
| Is This Answer Correct ? | 5 Yes | 7 No |
Answer / genset
"Genset Engineering Calc" (with Electrical & Engine
calculators) - iPhone + iPad + iPod App -
1. Can do more than 40 types of electrical & engine
calculations.
2. Calculation Formulas
3. Save & load calculations
4. Share the calculations via mail & SMS
5. & more ….
App download link -
http://itunes.apple.com/en/app/genset-engineering-calc/id551386320
If you like the app pls like it at -
http://www.facebook.com/pages/Genset-Engineering-Calc/267890853325587
| Is This Answer Correct ? | 0 Yes | 2 No |
Dear vivak
first , we see.what is EER of used ac system , if ac EER
is 8. ac load less 20% .
then
1.5 ton= 18000 btu = 5.250kw
20 nos. acs load =20*5.250KW
= 105 KW
DG pf is 0.8 and DG safty margine is 20%.
than 105*1.4=147KVA
we use 150kva DG and more .
| Is This Answer Correct ? | 2 Yes | 5 No |
can someone explain that how the speed of the protection system affects the fault level calculation?
I want formula to calculate cable size as per load given in length & amp. I searched many sites but didn't right answer. Please reply me asap.
what is the method to calculate the voltage drop for number of meters Example 250volts I/p at one end if the cable length is 50 meters what could be the drop?, after 100 meters how much? needs formulae.
What is the difference between lubricating oil and insulating Oil?
compressor compresses air means exactly what happens?
What is the operating range of voltage and current in grid supply in India?
If I want to use capacitor banks at HT (11 KV) side for maintaining power factor then which type of capacitor should I use? Plz give me the specification?? (I am using 1250 Kva transformer (11 KV/433V)).
200-100/1-1A – Transformer Knee point voltage
What is the output voltage of a DG set.
When we synchronize the Generator BKR with TIE BKR then Gen BKR is hold but TIE BKR is Tripped on Non directional over current but when TIE BKR is Syn. with Gen. BKR then no fault occur so what is the problem
explain working principle of earth leakage relay
0 Answers Divis Laboratories, SMIORE,
how to calculate singlephase motor efficiency?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)