Answer / vivek sri
A correction to my earlier answer(8)
In case we are to use a 3 phase generator then the total
current of 218.75 has to be equally shared between the 3
phases i.e. Iph=218.75/3=72.9 Amps.
So the genset rating would be again 52.5kVA(1.732*415*72.9).
But in actual as the number of AC's is 20;
18 Ac's get distributed equally (6 on each phase L-N) and
the balance 2 nos will be on one phase each.
So the max current will be 76.58 (18/3*10.94+10.94).
So the 3 phase genset rating would be 55kVA (1.732*415*76.58)
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / avnish sharma
I do agree with Mr. Prakash. but he has not considered pf, safety margin, and Future accommodation.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / girijapati mishra
TOTAL REF LOAD =1.5X20 =30 TR
1 TR = 3.5 KW
Thus , 30 TR = 105 KW
COP (i.e ratio of heat removed vs power input ) for AC
varies from 2.5 to 3 depending on design and other
considerations.
Assuming a COP 2.5 ( lower side)
Power required will be 42 kw (=105/2.5).
Considering power factor 0.8 ( gen assumption for all
caculations) rating of the DG set will be 52.5kva ( =42/0.8)
. A DG set higher than this calculated value to to selected
for this requirement.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / sathish reddy
45 KVA Diesel Genset is requied. Calculation is as follows,
20 * 1.5 = 30
Multiply by the MF 1.4
i.e. 30*1.4 = 42 KVA
As after 40 KVA we have 45 KVA as next higher capacity we
have to go by 45 KVA.
| Is This Answer Correct ? | 25 Yes | 22 No |
Answer / lokesh thota
Actually a 1.5tonn a/c will take 15amp at its maximum level
on 220v supply.so,for 20 such ac's you will need around 300
amps from that you can calculate how much Kva d.g u r need
with according to the vol you r selecting
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / jenifer
"Genset Engineering Calc" Version 1.1 is well designed than 1.0
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / prakash suhane
Total Load in T.R = 20X1.5 =30 T.R
1 T.R = 3.5 kw
for 30 T.R 30 X 3.5 = 105 K.w
any D.G set available more then 105 KVA is suitable for
this application.
| Is This Answer Correct ? | 16 Yes | 17 No |
Answer / jagjeet
Dear vIVEK,
Avinash has given correct answer , Generally pf of the
Dg Set is 0.8 and for calculation we are taking 20 %
Pf of Dg set is ==0.8
Safety Marging = 20 %
Future Expansion =20%
so 1.4*105/0.8=183KVA so you will have to go for 180 KVA
DG Set.
| Is This Answer Correct ? | 5 Yes | 7 No |
Answer / genset
"Genset Engineering Calc" (with Electrical & Engine
calculators) - iPhone + iPad + iPod App -
1. Can do more than 40 types of electrical & engine
calculations.
2. Calculation Formulas
3. Save & load calculations
4. Share the calculations via mail & SMS
5. & more ….
App download link -
http://itunes.apple.com/en/app/genset-engineering-calc/id551386320
If you like the app pls like it at -
http://www.facebook.com/pages/Genset-Engineering-Calc/267890853325587
| Is This Answer Correct ? | 0 Yes | 2 No |
Dear vivak
first , we see.what is EER of used ac system , if ac EER
is 8. ac load less 20% .
then
1.5 ton= 18000 btu = 5.250kw
20 nos. acs load =20*5.250KW
= 105 KW
DG pf is 0.8 and DG safty margine is 20%.
than 105*1.4=147KVA
we use 150kva DG and more .
| Is This Answer Correct ? | 2 Yes | 5 No |
What is Phase to Phase clearance for 800V System Operating Voltage as per IEC61439
we touch other end of the tester supply, why do not get shock?
How many devices can be connected in one zone of FACP
What is transmission line potential gradiant?
For R-L or R-C ckt,time constant formula is L/R and RC respectively and its unit is in sec.Pls tell me the derivation
How to calculate battery back up time for a 400 AH battery bank installed in telecom shelter for a load of 20 Amps and time taken to fully charge this battery bank?
A three phase transformer 460v primary 220v secondary (three phase four wire system.) Why did we get 460 volts across the neutral on the secondary side?
How many types are using in 220kv/400 kv swith yard
wat s the electronic device used in the fan regulators recently?
Meggering minimum acceptable Ohms for insulation resistance.
Pl. give me checklist for installation & commissioning of machine tool.
why transformer tank is in rectangular shape what happen when it is in step shape
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)