How Much Capacity of Diesel Genset is suitable for
20 no.s of 1.5ton AC's & Why?(Load Calculation)
Answers were Sorted based on User's Feedback
Answer / vivek sri
Lokesh Thota & Girijapati Mishra are partly correct
1.5 Tons=5.25KW (1Ton=3.5kW)
Assuming COP of 2.5 Input KW = 5.25/2.5=2.1kW
If the AC is rated for 240 volts then
I=(2.1*1000)/(240*0.8)=10.94 Amps where 0.8 is the power factor.
For 20 Ac's I=10.94*20=218.75
In case you are using single phase generator with rated
voltage of 240 volts then the required genset capacity is
=240*218.75/1000=52.5kVA.
In case you are using a 3 phase generator with voltage
rating of 415 volts (L-L, Line to neutral voltage will be
240 Volts) then rating would
be=1.732*415*218.75=157kVA(1.732 is SQRT 3)
Is This Answer Correct ? | 1 Yes | 6 No |
hello everybody...i m an Elelctrical Engineering student.. i m in final year.. i m attending IOCL interview on 2nd aug. kindly let me know on wat subjects to concentrate more...any body who has attended the interview can help... others can also post their views... thankyou.
examples of resistive inductive and capacitive load
what will be fault level of 11 KV , 2000 A ELECTRICAL SYSTEM?
I have a transformer whose primary operates at 230V, 50Hz for which the secondary voltage will be 12V, 50Hz. What will be the secondary voltage if the primary is fed with 400V, 8KHZ Signal?
IF WE SELECT THE 60H FREQUENCY IN INDIA WHAT WILL THE GOOD AND BAD EFFECT ?
HOW TO CALLICULATE RESITENCE,REACTANCE AND IMPEDENCE VOLTGE OF TRANSFORMER 13.33 KVA 144/240 VOLTS 93/56 A WITH FORMULA
how load of a turbo generator can be increased
Who is reputed manufacturer of TNC switch for ACB in India ?
what is the circutor?why we use it ?
The synchronous machine excitation system explain
what is meant by impedence? can you describe easy becuse iam not well familier in electrical?
What kind of battries are generaly used with Disel Generator?