How to select the cable size for the given load ?Pls
explain the Formulae
Answers were Sorted based on User's Feedback
Answer / sree
presuming, the unit of load is in HP(It is out put power)
output in KW= 735.5xHP(A).
Input in KW= A/Effy.(B).
Current= B/((1.732 * V * 0.7) (for 3 Phase star connected
load)(C)
Starting current= (1.5 to 2 times of full load current
(approx.)(D)
Based on cable catalague the size of cable will be chosen
as per above current rating(D).
or
Presuming the load is in KW(It is input power)
current=KW/((1.732 * V * 0.7) (for 3 Phase star connected
load)(A).
Starting current= (1.5 to 2 times of full load current
(approx.)(B)
Based on cable catalague, the size of cable will be chosen
as per above current rating(B).
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / vinay
Depending on amps rating.
A=P/V (for 1phase. P=Power in W, V=Voltage)
A=P/(1.732 * V * 0.7) (for 3 Phase)
| Is This Answer Correct ? | 6 Yes | 7 No |
Answer / jagjeet
Dear Mannu/ Vinay
Efficiency has to be considered for the system also.
| Is This Answer Correct ? | 1 Yes | 4 No |
what are smoke detectors ?
4 Answers Indian Military Services,
all types of electrical quations
Benifits of 3ph 4 wire metering over 3ph 3 wire
what is the difference between an alternator and a synchronous motor
hi frienda We have 250kva cater pillet dg set we are fasing one diffrent proublam in dg we are start dg set after one mint applying load around 450a load but dg was run 3 Or 4 mints after 3 mints dg was shuding down automatic how to face this proublam pls tel any budy
100V supply is appllied between 500K Resistance bulb. for 1 kwh energy, how long time the bulb will glow? explain the calculating method.
why ups rating in kva? and why ups are in parellel?.why isolation transformer is used in ups?
What is minimum permicible value of leackage current for LT Panle when applying voltage up to 3 KV for 5 Minuits?
prefer any good electrical engineering book.....it should be useful in the practical fied?
The capacity of the transformer is 20/25 MVA, Ratio is 132/11 KV, Vactor group YNyno. and impedance is 10.07%. As per the calculation the secondary current is 1312.2Amps. The maximum fault current the transformer should sustain is 13.030KA. How many times the transformer should sustain the maximum short circuit current of 13.030KA over a period up 1 Year. The transformer is repaired one & 10 Years old.
How to identify the start and end of 3phase 12 lead motor if U1, U2, etc numberings are lost or erased.
Will u plz give me simple diagram for tube light connection & also function of chock?
8 Answers Bhushan Power Steel, Dalmia Group, Jindal, Practical Viva Questions, TCS, Windmoller,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)