How to select the cable size for the given load ?Pls
explain the Formulae
Answer Posted / sree
presuming, the unit of load is in HP(It is out put power)
output in KW= 735.5xHP(A).
Input in KW= A/Effy.(B).
Current= B/((1.732 * V * 0.7) (for 3 Phase star connected
load)(C)
Starting current= (1.5 to 2 times of full load current
(approx.)(D)
Based on cable catalague the size of cable will be chosen
as per above current rating(D).
or
Presuming the load is in KW(It is input power)
current=KW/((1.732 * V * 0.7) (for 3 Phase star connected
load)(A).
Starting current= (1.5 to 2 times of full load current
(approx.)(B)
Based on cable catalague, the size of cable will be chosen
as per above current rating(B).
| Is This Answer Correct ? | 1 Yes | 1 No |
Post New Answer View All Answers
what is the use of expulsition protective gap in 11Kv line.
what is the effect of vector group while phase sequence of a generator changes,whether the vector group changes or not
1.what is the difference between ct and cvt? 2.what is the difference between pt and cvt? 3.what is the difference between relays and circuit breakers?
any earth foult trip the relay but in welding time not trip by earth foult
What is the type of feedback used in an op- amp schmitt trigger?
why the pf of semiconductor device is improved the electrical devices
kVA rating of ordinary transformer is increased when connected as an auto transformer because A transformation ratio increased B secondary voltage increased C energy is transferred both inductively and conductively D secondary current increased
Is there any guideline say about display of earthing value near to earth pit
to vary valtage from 0 - max a variac is necessary . so how to design for high power applications nearly about 200KW power
WHAT IS MEANT BY SHEATH VOLTAGE IN 132Kv cable?
how we decide scurt (disc) of insulator with respect to kv rating
What are the three major categories of error?
How would you calculate power loss in a resistor?
11KV AND 22KV NETWORK KW CAPACITY IN RING AND RADIAL?
Why we use Electrical energy rather than any other type of energy, mostly? Explain behavior of open secondary CT and short circuited secondary PT in energized condition?