what is different the DOL Starter and Star Delta STARTER

Answers were Sorted based on User's Feedback



what is different the DOL Starter and Star Delta STARTER..

Answer / natarajanramkumar

D.O.L Starter=Direct On Line Starter
1.It does not decrease the starting current.
2.It is cheap.
3.It connects directly the motor with supply for starting
as well as for running.
Star-Delta Starter
1.It decrease the starting current to 1/3 times.
2.It is costly.
3.It connects motor first in star at the time of starting
then in delta for running.

Is This Answer Correct ?    257 Yes 16 No

what is different the DOL Starter and Star Delta STARTER..

Answer / shankar rao

DOL is Direct on line starter, it is used upto 50 H.P Motors
Star delta starter is Starting time Motor Phases are in Star
and Running time it is convert to Delta scheme.( Because
High H.P Motors are Starting time we are appling Low voltage
by using Star system, and it is increase the Torque.)

Is This Answer Correct ?    161 Yes 92 No

what is different the DOL Starter and Star Delta STARTER..

Answer / ramanjaneyulu

DOL MEANS DIRECT ON LINE STARETER WE CAN USE DOL UP TO 5KW
RATEING IT CONNECTED DIRECT TO THE SUPPLY THROUGH OVER
LOAD RELAY IT DOES NOT REDUSE THE STARTING CURRENT. star
delta are used havy rateing motors because it limits the
starting current in 1/3 tmes of starting current

Is This Answer Correct ?    50 Yes 8 No

what is different the DOL Starter and Star Delta STARTER..

Answer / shafiq

in star/delta we can limit the current .but during starting
of motor in DOL motor will draw 3-5 time of its FLA

Is This Answer Correct ?    79 Yes 42 No

what is different the DOL Starter and Star Delta STARTER..

Answer / sunil guru

DOL-- As its meaning suggests "DIRECT ON LINE" the motors are provided the direct supply without any changes & this starters are only used for protection purpose (not for soft starting of the motor)and are preffered only upto 10 Hp motors in industries....

STAR DELTA--- are preffered beyond DOL range
first reduced voltage(1/3 of supply V) is given to the motor & as it reaches 70-80% of its rated speed full V is given. (it is the function of changing 4m star to delta)is done to reduce the starting current and to protect the motor.......

for any disagreement mail me at parmar20072008@yahoo.com

Is This Answer Correct ?    38 Yes 8 No

what is different the DOL Starter and Star Delta STARTER..

Answer / panil ahir

DOL is just running protection of motor while star-delta is running and starting protection of motor. It reduces the starting current of motor by increasing the resistance value of coils. As the starting resistance value is doubled the actual coil resistance, starting current reduces 1/3 times to protect the motor coils. 

Is This Answer Correct ?    10 Yes 1 No

what is different the DOL Starter and Star Delta STARTER..

Answer / rohan k trivedi

DOL MEANS DIRECT ON LINE STARETER WE CAN USE DOL UP TO 110
KW MOTORS SPECIALLY WHERE THE STARTING TOURQUE IS LOW AND
STARTING KICK IS ALSO SMALL. WHILE STAR DELTA IS DESIGN TO
REDUSE THE HIGH STARTING KICK. GENERALLY FANS BLOWER AND
COMPERSSOR MOTORS HAVE HIGH STARTING CURRENT DURING THE
STARTING SO IT IS GOOD TO USE STAR DELTA INSTEAD OF DOL.
ANOTHER DIFFERENCE IS THAT DOL HAS ONLY ONE CONTACTOR WHILE
STARDELTA HAS THREE CONTACTOR.

Is This Answer Correct ?    48 Yes 40 No

what is different the DOL Starter and Star Delta STARTER..

Answer / mallikarjun

the dol is direct online ie if press the start button it
start direct by closing the single contactor.and star-delta
starter is by redusing the volatge this will helps to
incrase the traque.

Is This Answer Correct ?    23 Yes 20 No

what is different the DOL Starter and Star Delta STARTER..

Answer / j.karthik

DOL Starter :
This starter is costwise cheap. it doesnot reduce the
starting current of the motor. The starting current of the
DOL starter is 6 to 7 times of the full load current. We can
use this starter for any higher kW range motors also even
6400kW motor.(In my working place using this DOL starter for
this 6400kW motor.

Note: for any standard cannot mentioned this much of the kW
motors only use in this type of starter nu..

Star/Delta Starter :
This starter is costwise higher. It can reduce the
starting current of the motor. The starter current of the
star/delta starter is 3 to 5 times of the full load current.
Generally in my working place this starter can be use above
75kW motors.

Is This Answer Correct ?    23 Yes 24 No

what is different the DOL Starter and Star Delta STARTER..

Answer / bathabile

DOL is a soft starter

Is This Answer Correct ?    1 Yes 12 No

Post New Answer

More Electrical Engineering Interview Questions

How is the Depth of Stator Slot being calculated for Synchronous Generator?

2 Answers  


how to convert the KVAR to microfarad??????????????????

2 Answers  


sir, I am from EEE branch.On feb 17 iam going to write an Exam for hindustan petrolium corporation Ltd.So plz send me the written exam pattern/Q's/interview questions.please mail to eee_dharmendra@yahoo.com

0 Answers  


When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct from supply and the other wire to the new earthing provided.If the bulb glows then the earth is ok.Else earth connection is not Ok. So, why dont we can use all the home appliances taking a single wire from the phase and the return connection to Earth instead of return connection to neutral?

2 Answers  


i have a roll dia aprox.43 inches and gear box ratio is 14.3.so my question is how was decide the kw rating of motor.

1 Answers  






How to determine the Power factor is Leading,Lagging & Unity ?.I don'thave any Meters.

3 Answers  


Why power genaration in India is at 50HZ while America its 60HZ

0 Answers   TATA,


What is the maximum breakdown voltage of 11KVA and 66 KVA power line and how it is calculated?

0 Answers   Anglo Platinum, Narnarayan Electrical,


what is saturation kit?which use above 15 kw motors panel side.

0 Answers   Power Grid,


We are getting supply at33kvand it stepdown to 11kv.So Our requirement is 11kv voltage.why we draw 33kv from the grid instead of 11kv?

2 Answers   Birla,


How to calculate the fuel consumption for 600kva DG genset which connecting with 25%load?

0 Answers   Debbas, GE, TCS,


i want the formula of total eletical knowledgement

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)