Answer / natarajanramkumar
D.O.L Starter=Direct On Line Starter
1.It does not decrease the starting current.
2.It is cheap.
3.It connects directly the motor with supply for starting
as well as for running.
Star-Delta Starter
1.It decrease the starting current to 1/3 times.
2.It is costly.
3.It connects motor first in star at the time of starting
then in delta for running.
| Is This Answer Correct ? | 257 Yes | 16 No |
DOL is Direct on line starter, it is used upto 50 H.P Motors
Star delta starter is Starting time Motor Phases are in Star
and Running time it is convert to Delta scheme.( Because
High H.P Motors are Starting time we are appling Low voltage
by using Star system, and it is increase the Torque.)
| Is This Answer Correct ? | 161 Yes | 92 No |
Answer / ramanjaneyulu
DOL MEANS DIRECT ON LINE STARETER WE CAN USE DOL UP TO 5KW
RATEING IT CONNECTED DIRECT TO THE SUPPLY THROUGH OVER
LOAD RELAY IT DOES NOT REDUSE THE STARTING CURRENT. star
delta are used havy rateing motors because it limits the
starting current in 1/3 tmes of starting current
| Is This Answer Correct ? | 50 Yes | 8 No |
Answer / sunil guru
DOL-- As its meaning suggests "DIRECT ON LINE" the motors are provided the direct supply without any changes & this starters are only used for protection purpose (not for soft starting of the motor)and are preffered only upto 10 Hp motors in industries....
STAR DELTA--- are preffered beyond DOL range
first reduced voltage(1/3 of supply V) is given to the motor & as it reaches 70-80% of its rated speed full V is given. (it is the function of changing 4m star to delta)is done to reduce the starting current and to protect the motor.......
for any disagreement mail me at parmar20072008@yahoo.com
| Is This Answer Correct ? | 38 Yes | 8 No |
Answer / panil ahir
DOL is just running protection of motor while star-delta is running and starting protection of motor. It reduces the starting current of motor by increasing the resistance value of coils. As the starting resistance value is doubled the actual coil resistance, starting current reduces 1/3 times to protect the motor coils.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / rohan k trivedi
DOL MEANS DIRECT ON LINE STARETER WE CAN USE DOL UP TO 110
KW MOTORS SPECIALLY WHERE THE STARTING TOURQUE IS LOW AND
STARTING KICK IS ALSO SMALL. WHILE STAR DELTA IS DESIGN TO
REDUSE THE HIGH STARTING KICK. GENERALLY FANS BLOWER AND
COMPERSSOR MOTORS HAVE HIGH STARTING CURRENT DURING THE
STARTING SO IT IS GOOD TO USE STAR DELTA INSTEAD OF DOL.
ANOTHER DIFFERENCE IS THAT DOL HAS ONLY ONE CONTACTOR WHILE
STARDELTA HAS THREE CONTACTOR.
| Is This Answer Correct ? | 48 Yes | 40 No |
the dol is direct online ie if press the start button it
start direct by closing the single contactor.and star-delta
starter is by redusing the volatge this will helps to
incrase the traque.
| Is This Answer Correct ? | 23 Yes | 20 No |
DOL Starter :
This starter is costwise cheap. it doesnot reduce the
starting current of the motor. The starting current of the
DOL starter is 6 to 7 times of the full load current. We can
use this starter for any higher kW range motors also even
6400kW motor.(In my working place using this DOL starter for
this 6400kW motor.
Note: for any standard cannot mentioned this much of the kW
motors only use in this type of starter nu..
Star/Delta Starter :
This starter is costwise higher. It can reduce the
starting current of the motor. The starter current of the
star/delta starter is 3 to 5 times of the full load current.
Generally in my working place this starter can be use above
75kW motors.
| Is This Answer Correct ? | 23 Yes | 24 No |
why no load voltage is greater than full load voltage?
PLZ EXPLIN ABOUT CLASS PS CLASS CT .WHY THEY R DESINED AND FOR WHAT PURPOSE?WHY OTHER CT CANT BE USED AS PS CLASS CT? EXPLAIN IN SIMPLE LAUNGAGE IF POSSIBLE PLZ GIVE CIRCIT DIAGRAM?EMAIL-RAJ_SINGH_0376@SIFY.COM
WHEN SINGLE PHASE SUPPLY AS 220V, WHY THE 3 PHASE- 4 WIRE MEASURED AS 440 VOLTS INSTEAD OF 660 VOLTS (220 VOLTS PER PHASE i.e 220x3 = 660 volts ).
Why we use a H.T. Fuse from a thick wire, on other side we use high rating of cables? & Why we use less Sq. mm Cable on H.T. side , on other side we use Large Sq. mm cable?
what is the knee point voltage ? what is differtial rela? what is impedance and % of impedane? what is the postive phase sequance ? negative phase sequane ? and zero sequance impedance ? what is sortcircuit calculaion? why take calculation? define stabilty test ? why? what sentivity test? define merz protection ? what is the burden ? class 5p10, accracy, metering ct take knee point voltage test thet time what heppan why dont take knee point test to metering ct?
WHAT IS MEANT BY TV TERMINAL IN 500MVA TRANSFORMER?
why the undervoltage relay's interlock is used in earthswitch closing operation of the 400kV line scheme?
Ohm's law applicable for semi-conductors?
What is a soft start?
What are the function of different components of servo motor?
what is difference between fuse and circuit breaker?
what is meaning of bus raiser???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)