what is different the DOL Starter and Star Delta STARTER
Answer Posted / natarajanramkumar
D.O.L Starter=Direct On Line Starter
1.It does not decrease the starting current.
2.It is cheap.
3.It connects directly the motor with supply for starting
as well as for running.
Star-Delta Starter
1.It decrease the starting current to 1/3 times.
2.It is costly.
3.It connects motor first in star at the time of starting
then in delta for running.
| Is This Answer Correct ? | 257 Yes | 16 No |
Post New Answer View All Answers
What are the advantages of instrument transformer?
what is the minimum (Common factor) insulatin resistance of the following a, 4mm sq wire b, cable from 50 mm sq to 800mm sq
If one lamp connects between two phases it will glow or not?
PAC and simple Ac different
from where the self excitrd induction generator get the power?why is the voltage regulation is poor of seig?
Is it a better option to procure screw type air compressor rather than reciprocating air compressor?If so, what is the reason?How should we select an air compressor(100 CFM)? Please mention the important parameters of air compressor.
why wire sizes are 3/29 or 7/29 and why not wire sizes are 2/29 or 6/29?
List the time domain specifications.
What is the role of Dedicated earthing in UPS System?
can anyone give an idea about dia calculation in cold rolling mill
how to calculate the tarriff for an industry whose kva demand is 10 mva
What is the difference between a fuse and a breaker?
How to Calculate Current Rating of SDFU (Switch Disconnector Fuse unit) for Protectionof Capacitor Bank connected to Busbar of 800Amp,in LV side of 11/0.433KV, 250KVA Transformer?
How they LT panel busbar size choose
What are your personal skills and abilities for such a Master Course and your possible preparation to undertake this course?