Answer / c r venkatesh

Absolutely no problem.you can always use higher burden CT'
without any problem

Is This Answer Correct ?    11 Yes 1 No

My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there..

Answer / roy

Hi ,
Yes there is . and a highr rated VA is never recommented
for metering ( again it depends the accuracy but still not
used as per IEC)
Note:The accuracy class will not be guaranteed for burdens
above rated burden or below 25% of the rated burden.Check
IEC 60044
Amd more interstingly , we are allowing or excepting to
saturate this metering core during fault to protect the
metering Equipment reff. IEC 44

Is This Answer Correct ?    3 Yes 0 No

My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there..

Answer / chandru_williams

no problem at all when we increase the burden . But It
should be noted that the current ratio should not be
increased, since it leades to sensing problem which inturn
hinders the metering values.

Is This Answer Correct ?    3 Yes 1 No

My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there..

Answer / giri

No problem ,but the size of CT may increase.....

Is This Answer Correct ?    2 Yes 1 No

My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there..

Answer / anbuselvan

No problem.

Bcaz CT is an Instrumental Transformer(i,e.,Measurement of
High rating current) to measure only Current.

So there will be no of tapping for each range of current.So
that it will easily sense the rating which u set.

Here both your current rating is same.so no problem at all,
even if the voltage varies.

Is This Answer Correct ?    2 Yes 1 No

My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there..

Answer / satvinder kumar

50/5 1va is suitable for bar primary ct if you go for
higher 15 va then it is good to opt wound primary ct{WPL}
OTHERWISE THE SIZE OF THE CT WILL INCREASE

Is This Answer Correct ?    1 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

What is the difference between synchronous motor & asynchronous motor

2 Answers  


Can we use both Electrical & mechanical interlock between tow breakers? if yes how, please explain

0 Answers  


what is the function of avr when synchronous generator act as synchronous motor

1 Answers  


What is expand formation of AYFY cable

2 Answers   HP,


earth also having a gravitational force (magnetic field of north and south)but it attracts any object compare to this theartifical magnetic cant perform same as earth why?

0 Answers  






I have a 3 phase 600 volt prim. feed and a 120/208 sec. Isolateing tranformer .We are using this system for safety against shock . What is the proper grounding ?? Does the common on sec. get earth ground ???

1 Answers  


Draw a Block diagram of TWO UPS systems connected in Parallel in Paralled mode?

0 Answers   HSL,


How we calculate the current carrying capacity of H.T. cabel?

0 Answers   Bhel,


How Humming noise generated in starter motor which was used the start the engine in a vehicle/car/Truck?.Moreover Starter motor was operated in DC power supply. Can you guys clarify ?

2 Answers  


what is the proximity & ferranti effects can you explain to me

1 Answers   APTransco,


WHEN I AM CONNECTIN TWO ELCB IN PARALLEL.ONE ELCB TRIPPED...HOW IT HAPPEND??

5 Answers  


Do closed loops systems require manual input?

0 Answers   Ericsson,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)