My requirement is 1VA,50/5A Current Transformer for
Metering .If I select 15VA , 50/5A CT.Is there any
possibility of Technical Problem ?
Answers were Sorted based on User's Feedback
Answer / c r venkatesh
Absolutely no problem.you can always use higher burden CT'
without any problem
Is This Answer Correct ? | 11 Yes | 1 No |
Answer / roy
Hi ,
Yes there is . and a highr rated VA is never recommented
for metering ( again it depends the accuracy but still not
used as per IEC)
Note:The accuracy class will not be guaranteed for burdens
above rated burden or below 25% of the rated burden.Check
IEC 60044
Amd more interstingly , we are allowing or excepting to
saturate this metering core during fault to protect the
metering Equipment reff. IEC 44
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / chandru_williams
no problem at all when we increase the burden . But It
should be noted that the current ratio should not be
increased, since it leades to sensing problem which inturn
hinders the metering values.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / anbuselvan
No problem.
Bcaz CT is an Instrumental Transformer(i,e.,Measurement of
High rating current) to measure only Current.
So there will be no of tapping for each range of current.So
that it will easily sense the rating which u set.
Here both your current rating is same.so no problem at all,
even if the voltage varies.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / satvinder kumar
50/5 1va is suitable for bar primary ct if you go for
higher 15 va then it is good to opt wound primary ct{WPL}
OTHERWISE THE SIZE OF THE CT WILL INCREASE
Is This Answer Correct ? | 1 Yes | 1 No |
What is the difference between synchronous motor & asynchronous motor
Can we use both Electrical & mechanical interlock between tow breakers? if yes how, please explain
what is the function of avr when synchronous generator act as synchronous motor
What is expand formation of AYFY cable
earth also having a gravitational force (magnetic field of north and south)but it attracts any object compare to this theartifical magnetic cant perform same as earth why?
I have a 3 phase 600 volt prim. feed and a 120/208 sec. Isolateing tranformer .We are using this system for safety against shock . What is the proper grounding ?? Does the common on sec. get earth ground ???
Draw a Block diagram of TWO UPS systems connected in Parallel in Paralled mode?
How we calculate the current carrying capacity of H.T. cabel?
How Humming noise generated in starter motor which was used the start the engine in a vehicle/car/Truck?.Moreover Starter motor was operated in DC power supply. Can you guys clarify ?
what is the proximity & ferranti effects can you explain to me
WHEN I AM CONNECTIN TWO ELCB IN PARALLEL.ONE ELCB TRIPPED...HOW IT HAPPEND??
Do closed loops systems require manual input?