My requirement is 1VA,50/5A Current Transformer for
Metering .If I select 15VA , 50/5A CT.Is there any
possibility of Technical Problem ?
Answers were Sorted based on User's Feedback
Answer / c r venkatesh
Absolutely no problem.you can always use higher burden CT'
without any problem
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / roy
Hi ,
Yes there is . and a highr rated VA is never recommented
for metering ( again it depends the accuracy but still not
used as per IEC)
Note:The accuracy class will not be guaranteed for burdens
above rated burden or below 25% of the rated burden.Check
IEC 60044
Amd more interstingly , we are allowing or excepting to
saturate this metering core during fault to protect the
metering Equipment reff. IEC 44
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / chandru_williams
no problem at all when we increase the burden . But It
should be noted that the current ratio should not be
increased, since it leades to sensing problem which inturn
hinders the metering values.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / anbuselvan
No problem.
Bcaz CT is an Instrumental Transformer(i,e.,Measurement of
High rating current) to measure only Current.
So there will be no of tapping for each range of current.So
that it will easily sense the rating which u set.
Here both your current rating is same.so no problem at all,
even if the voltage varies.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / satvinder kumar
50/5 1va is suitable for bar primary ct if you go for
higher 15 va then it is good to opt wound primary ct{WPL}
OTHERWISE THE SIZE OF THE CT WILL INCREASE
| Is This Answer Correct ? | 1 Yes | 1 No |
if flux and load static in dc motor and supply voltage increases 20% then what happened in speed
how to calculate unit consumption on 3phase 380-415 v0lt kilowatt motor eg ( 55kw,380v,3phase 50-60hz)
What will happen if the armature resistance is in minimum position and the field resistance is in maximum position while starting the motor
What kind of maintenance is conducted for generator
What is the principal of motor?
why fuse not recomended to neutral
give single line diagram of D.G distribution form alternator to main L.T panel?
how to synchronize 4 nos. of diesel generator sets of different capacity (kva)?
what is impedance of transformer?
7 Answers Synergy, Vijai Electricals,
My system is 22kv/3.3kv transformer. client is asking to use NGR, but as we have dedicated Neutral Earthing systems which has a value less than 1 Ohm. So i want solid comparision. Why i should not use NGR as my system is already protected.Can any one help me to get out of this.how should i reply on basis of some great comparision and calculations. Please help
what s the differenc between electrical &electronis , how to define them
how we done power management?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)