My requirement is 1VA,50/5A Current Transformer for
Metering .If I select 15VA , 50/5A CT.Is there any
possibility of Technical Problem ?
Answers were Sorted based on User's Feedback
Answer / c r venkatesh
Absolutely no problem.you can always use higher burden CT'
without any problem
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / roy
Hi ,
Yes there is . and a highr rated VA is never recommented
for metering ( again it depends the accuracy but still not
used as per IEC)
Note:The accuracy class will not be guaranteed for burdens
above rated burden or below 25% of the rated burden.Check
IEC 60044
Amd more interstingly , we are allowing or excepting to
saturate this metering core during fault to protect the
metering Equipment reff. IEC 44
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / chandru_williams
no problem at all when we increase the burden . But It
should be noted that the current ratio should not be
increased, since it leades to sensing problem which inturn
hinders the metering values.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / anbuselvan
No problem.
Bcaz CT is an Instrumental Transformer(i,e.,Measurement of
High rating current) to measure only Current.
So there will be no of tapping for each range of current.So
that it will easily sense the rating which u set.
Here both your current rating is same.so no problem at all,
even if the voltage varies.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / satvinder kumar
50/5 1va is suitable for bar primary ct if you go for
higher 15 va then it is good to opt wound primary ct{WPL}
OTHERWISE THE SIZE OF THE CT WILL INCREASE
| Is This Answer Correct ? | 1 Yes | 1 No |
why transformer rating in KVA ?
8 Answers Bhel, TATA, Voltage,
what is hourly consumption of coal in therma plant
How much area is covered by a single lightning arrestor to protect object from lightning strokes ?
What is the difference btwn grounding and earthing?
what do you call the last pole on a overhead line near a substation
i am BSEE student, my project study is to synchronize the generator of an hospital, it have a one 313KVA standby-power diesel gen.,and three 100kva transformer.The generator system is operated manually and no ATS or UPS. one more new building is being build so the transformer will be upgrade to a higher vale. 1)how i can connect the new gen. to the old gen. and to the synchronize panel? 2)what is the new gen. to be buy?(rating, etc.) These is my title: To synchronize the generator system of the ____ Hospital. Anyone have a good title? Thanks.
difference between ground,neutral and earth?..
What is the effect of pd controller on system performance?
when giving a supply to wounded coil it will get magnetised, but the same is not if it is not wounded on a core..and it is getiing short....why.......
can we transmit power with out cable if it is possible how it is possible.
why some transmission lines have 7 wires n why some have 3 n 4??
Discuss the effect of sudden loading of an induction motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)