A three phase load, around 4 km away from the 11/0.433KV
distribution transformer (Neutral of Transformer is
solidily earthed) and consisting of mainly very costly and
sensitive electronic equipments is giving trouble due to
high voltage difference between neutral and body earth.
Whether this problem can addressed by connecting neutral at
the load point solidly to earth?
Answers were Sorted based on User's Feedback
Answer / parul
Check the load circuit properly.Check the transformer at
open and short circuits.Isolate the neutral earthing in the
substation transformer and check the voltage in all phases
to find out whether transformer is the problem or your load.
After considering all above checks you may do the earthing
of neutral point in your load.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / velusamy
check the overall earth pit resistance value and it
should be less than one ohms
| Is This Answer Correct ? | 1 Yes | 1 No |
It is an absurdity to try to provide 433 volt electrical
service to a load that is 4 KM away. You need to install 11
kv line to the load and then install the transformer. You
won't have a problem. There is always a difference between
the earth and a neutral. If that is a problem, bond them
together. They should be anyway.
| Is This Answer Correct ? | 0 Yes | 0 No |
why energy storing capacity of magnetic field is much higher than electric field ?
explain wiring system
how we calculate the knee point of a protection and metering CT and what is the testing procedure.
Why we are mostly using a single 3-phase transformer instead of three 1-phase transformers?
How many types of protection relays are there based on the characteristic?
what is the frequency standard with tolerance level for India?
What is pole slipping relay? When it is operated?
In view of Electrical Engg. What is the use of SCR(Silicon control rectifier)
Meggering minimum acceptable Ohms for insulation resistance.
which mm cable should be used for 1.hp immersible pump motor for the distance of 330 metres?
what is the application of dynamic Breaking resistor in inverter ? & How it works ?
whenever a squirrel or a crow gets tangled near the out put of the feild transformer there is a discharge of 440 volts of current through the neutral due to which my appliances blow up causing a huge bang.will the RCCB help in these conditions
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)