A three phase load, around 4 km away from the 11/0.433KV
distribution transformer (Neutral of Transformer is
solidily earthed) and consisting of mainly very costly and
sensitive electronic equipments is giving trouble due to
high voltage difference between neutral and body earth.
Whether this problem can addressed by connecting neutral at
the load point solidly to earth?
Answers were Sorted based on User's Feedback
Answer / parul
Check the load circuit properly.Check the transformer at
open and short circuits.Isolate the neutral earthing in the
substation transformer and check the voltage in all phases
to find out whether transformer is the problem or your load.
After considering all above checks you may do the earthing
of neutral point in your load.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / velusamy
check the overall earth pit resistance value and it
should be less than one ohms
Is This Answer Correct ? | 1 Yes | 1 No |
It is an absurdity to try to provide 433 volt electrical
service to a load that is 4 KM away. You need to install 11
kv line to the load and then install the transformer. You
won't have a problem. There is always a difference between
the earth and a neutral. If that is a problem, bond them
together. They should be anyway.
Is This Answer Correct ? | 0 Yes | 0 No |
I am going to appear RRB Sr. Section Engineer Exam, Electrical. Can you send me previous year questions of RRB Electrical engineer. specially Section Engineer questions. my email id is likerahulworld@gmail.com
why only 11kv level is used for transmission purpose? why not 230v?
what is the advantage and disadvantage of billing in kwh and kvah by electricity board .
What is resonant peak?
How to select batteries required for ups and the inverter if we Known load? And how AH is selected of battery?
Give accurate definitions for these electric terms: Inductor Inductance Inductive Induction Reactance Reactive Esam Baraka ٢١ ساعة
Generation of voltage for each phase are same of a turbogenerator.Although the short circuit current flow when two phase of turbogenerator are shorted(where current can't flow without potential difference),why?
what could be the reason of a burnt current transformer in an electrical panel
I want Primary side delta and Sec side Star connection transformer . but i have received Star - Star transformer ,shall i use the same transformer by giving the only 3 ph on Primary side without Neutral connection on the Starpoint.
what is the thumb rule for determination resistance of resistor?
How to calculate VCB rating for 33KV ,25 MW Power line?
Why we use three phase world wide why not four phase or five phase being used?