Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


A three phase load, around 4 km away from the 11/0.433KV
distribution transformer (Neutral of Transformer is
solidily earthed) and consisting of mainly very costly and
sensitive electronic equipments is giving trouble due to
high voltage difference between neutral and body earth.
Whether this problem can addressed by connecting neutral at
the load point solidly to earth?

Answers were Sorted based on User's Feedback



A three phase load, around 4 km away from the 11/0.433KV distribution transformer (Neutral of T..

Answer / parul

Check the load circuit properly.Check the transformer at
open and short circuits.Isolate the neutral earthing in the
substation transformer and check the voltage in all phases
to find out whether transformer is the problem or your load.

After considering all above checks you may do the earthing
of neutral point in your load.

Is This Answer Correct ?    1 Yes 1 No

A three phase load, around 4 km away from the 11/0.433KV distribution transformer (Neutral of T..

Answer / velusamy

check the overall earth pit resistance value and it
should be less than one ohms

Is This Answer Correct ?    1 Yes 1 No

A three phase load, around 4 km away from the 11/0.433KV distribution transformer (Neutral of T..

Answer / wareagle

It is an absurdity to try to provide 433 volt electrical
service to a load that is 4 KM away. You need to install 11
kv line to the load and then install the transformer. You
won't have a problem. There is always a difference between
the earth and a neutral. If that is a problem, bond them
together. They should be anyway.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

If one ct is reversely connected in Y system what will effect in kwh and kvarh meter?

1 Answers  


motor is 12.5hp after starting few minets motot get hot? why?

5 Answers  


why PT Primary are the grounded?

5 Answers   L&T,


What is systematic error?

0 Answers  


funtion of choke

4 Answers   L&T,


why are transformer rating in MVA

2 Answers   Suzlon,


How will you explain transformer action in case of 3-phase induction motor?

4 Answers  


where HT & LT capacitor uses ?

2 Answers   NTPC,


Differentiate between Low and High impedance Protection

1 Answers  


What is proportional controller?

0 Answers  


what is the purpose of shading ring or shading coil in electrical equipments.

0 Answers   BARC,


What is the minimum distance between taransformer (say 2000 kva)and its earth pit?

2 Answers   Bhel,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)