Explain REF protection and sbef protection in transformer?
Answers were Sorted based on User's Feedback
Answer / ranjith
It detects the faults of winding in neutral grounding side
Is This Answer Correct ? | 0 Yes | 0 No |
REF is restricted earth fault relay, for internal earth fault of Tr . SBEF is standby earth fault relay or backup for both internal and outside earth faults . The CTs of both are connected to neutral of Tr. Discriminative setting is required
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suresh
Ref is restricted earth fault, The relay was acted for winding to winding shorted with ground.
Is This Answer Correct ? | 0 Yes | 0 No |
i am using star-delta connections with reverse/forward direction motion of the 75hp induction motor.What should be the ratings of Main,Delta and Star contactors and why?
how braking & making capacity of circuit breaker is calculated?
why there is 1 phase and 3 phase but not 2 phase and 4 phase?
What is the effect of electric motor stuck in star configuration,
how many frequent start/stop operation possible in case of HT MOTORS.
What is the correct procedure to shutdown VCB in 11kv substation.safety and work procedure
define bilateral network and unilateral network? give an example.
why dimmerstate always connected in star connection? what will happen if it connected in delta?
why we are not giving the zone 1 trip command to the master trip relay
what are the usual topology of transformers at different substations in the power system and why that particular topology is choosen. what are the limitaions of that topology?
Determine the BTU size of an aircon for 20 sq metre room
how can we judge the percentage of load on the basis of temperature differences readings between WTI and OTI in a transformer