Explain REF protection and sbef protection in transformer?
Answers were Sorted based on User's Feedback
Answer / ranjith
It detects the faults of winding in neutral grounding side
| Is This Answer Correct ? | 0 Yes | 0 No |
REF is restricted earth fault relay, for internal earth fault of Tr . SBEF is standby earth fault relay or backup for both internal and outside earth faults . The CTs of both are connected to neutral of Tr. Discriminative setting is required
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suresh
Ref is restricted earth fault, The relay was acted for winding to winding shorted with ground.
| Is This Answer Correct ? | 0 Yes | 0 No |
Why is the electric shock from the DC supply is more dangerous than the shock from AC supply.
how to calculate the ngr capacity(nutral grounding resistor)
How many earthings are required for motors?
in 3 phase induction motor resistance value is how much
I have a one P.F meter in my factory showing 2 phase leading and one phase lagging then what is my actual P.F.
what is the abbreviation & meaning of UI charges
How is operate breaker failure scheme in substation
What is your acheivements
usually why bettery voltage are 1.5V, even if you open a 9V battery there are six 1.5V batteries in series. is it not possible to increase this voltage other than putting in series
what do u mean by bus bar?
If ac voltage applied to the field of dc generrator the output of dc generator ?
what should be distance between two electrical earthing pit as per i.e.e
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)