Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


we have taken HV test of 2.5 k and Megger test on 11 kv HT
cable.here it shows no fault but when we are charging the
same cable with 11 kv supply why the VCB 11 kv gets tripped
can anybody define the possible cause of fault ?

Answers were Sorted based on User's Feedback



we have taken HV test of 2.5 k and Megger test on 11 kv HT cable.here it shows no fault but when ..

Answer / shariff

The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...

Is This Answer Correct ?    4 Yes 1 No

we have taken HV test of 2.5 k and Megger test on 11 kv HT cable.here it shows no fault but when ..

Answer / shariff

The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...

Is This Answer Correct ?    1 Yes 1 No

we have taken HV test of 2.5 k and Megger test on 11 kv HT cable.here it shows no fault but when ..

Answer / nagesh.patwari

Check out the control circuit. And every possible relevant thing in panel cable breaker.... Thoroughly.

Is This Answer Correct ?    0 Yes 0 No

we have taken HV test of 2.5 k and Megger test on 11 kv HT cable.here it shows no fault but when ..

Answer / shariff

The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

what is the purpose of shading ring or shading coil in electrical equipments.

0 Answers   BARC,


Why electrical heaters are not provided with overload relays in circuits

1 Answers  


What is correction factor in Tan delta test?

1 Answers  


how the speed of the gets motor regulated. does it draw the same current on the all speed level.

0 Answers   Danko,


can u describe the method used for protection of transmission line.

0 Answers   IBM,


WHY IN THREE PHASE CABLE 440V CURRENT FLOWS IF IN ONE PHASE 230V CURRENT FLOWS ???

3 Answers  


A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is onbserved the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?

1 Answers  


What will happen if an AC induction motor is applied with DC voltage?????????Kindly give all the posssible answers...

2 Answers  


single phase voltage 230 and Three phase voltage 450 why 690 voltage

1 Answers   XYZ,


Dear sir my name Ankit i m Diploma holder present working in Welspun Corp ltd Anjar as Asst.engg (salary 14400/month ctc) i Would like to change my company also i have selected in ford India pvt ltd Sanand as trainee Tech with salary 12000/month so please suggest me for changing my job hope for *ve response

0 Answers  


if receiving voltage is higher than sending ones what will be the effect of receiver

4 Answers  


can we connect PARALLEL 2 D.G set with different rating?? How ? What is the requirement for this connections?

1 Answers   Amoli Organics,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)