we have taken HV test of 2.5 k and Megger test on 11 kv HT
cable.here it shows no fault but when we are charging the
same cable with 11 kv supply why the VCB 11 kv gets tripped
can anybody define the possible cause of fault ?
Answers were Sorted based on User's Feedback
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
| Is This Answer Correct ? | 1 Yes | 1 No |
Check out the control circuit. And every possible relevant thing in panel cable breaker.... Thoroughly.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
| Is This Answer Correct ? | 0 Yes | 1 No |
Which of the following are the important limitations of rod gap surge arresters? 1. They are not capable of selling off power frequency follow up current. 2. After a discharge, the rods are destroyed completely. 3. Performance is affected by climatic conditions. Use the following codes for selecting the correct answer. Codes: (a)1, 2 and 3 (b)1 and 2 (c)2 and 3 (d)1 and 3
how fluoresent lamp works??
what is divercity factor?
Why a single-phase induction motor not an inherently self-starting machine?
11 Answers ETC, Hindustan Shipyard,
The shot circuit in any winding of transformer result? Explain
What are the types of lighning arrestor protection system? how to choose that according to load?
What is different bewteen low or high impedance busbar protection scheme
why we use 50 hz frequency in india .. why not 60 hz
What are the procedures followed for underground cable laying.....???
What is the value of nuetral current in star connected load when DC is supplied to it???
what difference between thermal and bi-metal over load relay?
transformer 3 ph, 225 kva pri 480v, sec 208v. primary neutral connected to system, is secondary neutral to be grounded and how
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)