what happens if DG N earthing fails while running and N
Earthing fails while Transformer on load ???what will be the
impact ???????/
Answers were Sorted based on User's Feedback
Answer / pillay
sorry about the earlier answer.
if the DG or xformers load was balanced when the neutral
failed than there would had been no impact, B cause the
summation current is zero but if it was loaded with a
unbalanced load than the phase voltage would be unbalanced
and cause damage to single phase equipment. the single phase
voltage can raise up to phase to phase voltage depending on
the load current.
Is This Answer Correct ? | 4 Yes | 0 No |
In a voltage-controlled current source A A current booster is never used B The load is always floated C A stiff current source drives the load D The load current equals Isc
what is threshold voltage for a relay???what does it exactly means ?whats its value in our indian transmission system say 11kv feeder RMU relay
what happen if generator of micro hydro running at only a small percentage of its capacity, as a comparison, if the diesel generator that runs on only a fraction of its capacity there will be a wet stacking
HOW TO CONNECT THREE PHASE OVER LOAD RELAY FOR SINGLE PHASE
How can we measure MVAR of a 3 phase transformer.....???
Z transform is use when system is not a) converges b) diverges
in control panel, how can i measuring the distance between one bus bar to another bus bar. then now only for bus bar. in mpcb and contactor also. that means one mpcb to another mpcb how much distance? how can i calculate that.
Draw a SLD for main panel for school having connected load of 1200kw and emergency generator 200kw.also show the increase of additional load of chiller 225kw in the lv panel indicating meter postion size of transformer ,cables and capacitor bank.
Explain the method to keep noises low in a control system?
What is FM200 Fire Supresion System??
we are using three transformer 33000/430 vac for three separet block.all three transformer have three LT panel separetly. can be Interconnected all three panel through bus coupler. this is permissable or not by state electricity board.
Why the underground cables will Punchar? or what is the reason to burst the underground cables?