I am working on a 11KV system with fault current of 40KA
for 1 second. I have selected 2500MVA 11/0.433KV
transformer.
How can i find the impedance value for this transformer?
Please help me.
Answers were Sorted based on User's Feedback
First I do not believe an 11 kv system can have a 40ka
fault. You need to check again.
Second I do not believe you can connect a 2500 mva
transformer to an 11 kv system. Maybe 2500 kva.
%Impedance is on the nameplate of the transformer or ask
the manufacturer.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kaushik
i don't understand the purpose of giving 1 second ......
but what i think solution will be
s.c mva=1.732*v*i.
s.c mva=1.732*11000*40000.
s.c mva=762.08 mva.
per unit impedence of the transformer will be= (base
mva)/(s.c mva)
taking transformer 2500kva(i think it is wrong 2500mva)
we get
=(2.5/762)*100=0.328% of tranformer impedence
Is This Answer Correct ? | 0 Yes | 0 No |
How many points does a Circuit can have?
what are the pecularity of shaver sockets ?
how much cable size required for 70 kilowatt load.
Why electrons flow only one direction in semiconductors. why can not flow both directions
WHY IS CT SECONDARY SHORTED TOWRDS TH EQUIPMENT TO BE PROTECTED
hi can you give any body fault level calculation, generator fault level calculation,transformer fault level calculation for system fault level with equation? i have 3.3kv generation voltage three gas gen sets, one is 1.9MW,2nd is 2.5MW,& 3rd is 3.8MW & i have 11 kv generation voltage one gas gen sets is 3.8MW, we are step up to 22kv by transformer
3 Answers Hindalco, Piramal Healthcare,
Equal resistance of 100ohm each are connected to the arms of whestons bridge, which is supplied by 2v battery. The galvanometer can sense a current low as 1microAmp. What is the smallest resistance that can be measered.
What are the special protection given for high capacity Motor, more then 10mw
what is the basic principle of the alternator ????
do we use links in a dc circuit?if so what s its use in it?
to hook up ten 50 amp rv pedastels at a lenth of 600 feet from the service what size will my service need to be and the size of wire will I have to run to each pedastel in series??????
types of motor starter