Answer / kayode j.
The anti-pumping relay is a device in circuit-breaker whose
function is to prevent multiple breaker closures. For
instance, if the operator gives the closing command to the
breaker by pressing the close button and the breaker
closes. However, a fault in the system causes the breaker
to trip. Since the close command is still in the pressed
condition, there is a chance of the breaker closing again
and being tripped by the relay multiple times. This can
damage the closing mechanism of the breaker. The anti-
pumping relay prevents this by ensuring that the breaker
closes only once for one close command from the control
panel.
| Is This Answer Correct ? | 248 Yes | 12 No |
Answer / pundlik wanwe
Anti pumping relay is provided with closing circuit of
Circuit Breaker, which prevents the repetitive closing
command to the breaker.
| Is This Answer Correct ? | 196 Yes | 24 No |
Answer / chirag
when breaker is close at one time by close push button,the
anti pumping contactor prevent re close the breaker by
close push button after if it already close.
| Is This Answer Correct ? | 75 Yes | 23 No |
Answer / mostafa
suppose you close c.b and fault happen during closing (
temporary earhtg , breakdown ...) and you still press the
push botton the breaker will reclose in fault agian so
regard for this anti pumping used to prevent reclose
| Is This Answer Correct ? | 66 Yes | 18 No |
Answer / vale
The anti-pumping relay is a device in circuit-breaker whose
function is to prevent multiple breaker closures. For
instance, if the operator gives the closing command to the
breaker by pressing the close button and the breaker
closes. However, a fault in the system causes the breaker
to trip. Since the close command is still in the pressed
condition, there is a chance of the breaker closing again
and being tripped by the relay multiple times. This can
damage the closing mechanism of the breaker. The anti-
pumping relay prevents this by ensuring that the breaker
closes only once for one close command from the control
panel.
| Is This Answer Correct ? | 40 Yes | 6 No |
Answer / vimalraj
If the closing coil circuit (52/CC) is continuously
energized, the anti-pump relay ensures that the circuit
breaker does not “pump” open and closed in the event that a
trip signal is also present. The anti-pump relay
performs this function by allowing the closing coil to
activate only if:
• the circuit is energized
• the drive springs are fully charged, and
• the motor relay is de-energized
The anti-pump relay activates when the close circuit and
motor relay are energized.
If the close circuit is energized continuously, the
anti-pump relay will be latched
in the energized position after the motor relay is
de-energized by a pair of its own
normally open contacts. When the anti-pump relay is
energized, a pair of its
normally closed contacts, in series with the closing coil,
ensure that the closing
coil cannot be energized. The closing coil activates only
when the closing circuit is
de-energized (de-energizing the anti-pump relay), then
closed again
| Is This Answer Correct ? | 26 Yes | 3 No |
The function of closing coil is to close breaker,it is
designed to take supply for few seconds,if we give
continuous supply to it burns,so to prevent burning of
closing coil,after closing of breaker closing coil must be
bypass,and this is done by made arrangement for bypassing
closing coil after breaker closure,
so if above condition is achieved and then breaker is close
,we can not operate closing coil and it is prevented from
burning ,this system is called anti pumping
thanks
| Is This Answer Correct ? | 31 Yes | 12 No |
Answer / sangeetha.np
The circuit breaker can be operated from panel, if they are
simulated it can be operated from computer, and in the
local mode also, this anti pumping provides protection
against multiple closing of breaker. Once the breaker is
closed in any of these modes it wont accept it another
time,as it can be operated in many ways.
| Is This Answer Correct ? | 20 Yes | 8 No |
Answer / mohamed elias
The anti-pumping relay is a device in circuit-breaker whose
function is to prevent multiple breaker closures. For
instance, if the operator gives the closing command to the
breaker by pressing the close button and the breaker
closes. However, a fault in the system causes the breaker
to trip. Since the close command is still in the pressed
condition, there is a chance of the breaker closing again
and being tripped by the relay multiple times. This can
damage the closing mechanism of the breaker. The anti-
pumping relay prevents this by ensuring that the breaker
closes only once for one close command from the control
panel.
| Is This Answer Correct ? | 14 Yes | 2 No |
what is tan delta point in a current transformer?
In 1000KVA Transformer why does we connect HT with delta connection and LT with star connection.Illustrate by showing formula?
what is the preventive maintence for ht panels and busbars and vcb abd acb's.
if two transformers are placed parallel & both have fault impedance of 50KA will it increase or decrease show example?
some practicle study shows that the reactive power at the receiving end is not equal to the reactive power at the sending end.But according to theory the reactive power is exchanged by different parts of the network – capacitors and reactors permanently, but is never consumed or produced. Then Where that reacrtive power loss occuring?is there any formula to calculate reactive power loss?
my field of interest is T&D. plz tell something about that.
What is super thermal power plant? and how it will differ from normal thermal power plant
difference between isolater and circuit breaker?
what you mean by current? what you mean by voltage? what is difference between star and delta connection in motor side?
what is the clearance time circuit breakr?
During the testing of Electrical Equipment the test cables should not touch the equipments. For that testing engineers use to cotton rope to hang the cable from measuring Equipment to testing equipment terminal. Please explain the technical reason for this practice.
How a Universal motor works in Both A.C and D.C? What is the constructional difference with other single phase motors?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)